    Default minimum height for laundry standpipe?

    Under UPC the laundry standpipe p-trap must be: 6" <= floor <= 18"
    Q1: where is the measurement taken from w/ regard to the p-trap? In Peter Hemp's book it shows it as the connection point between the standpipe (above) and the p-trap (as opposed to the weir or dead bottom of the p-trap, to name to other obvious points of reference). Is Hemp's drawing correct?

    Under UPC the laundry standpipe top must be: 18" <= p-trap <= 30"
    Q2: is the aim of these two restrictions to end up with the standpipe at 36"? One interpretation would be that if the p-trap is 6" from floor, standpipe should be 30" from p-trap, and if p-trap is 18" from floor standpipe should be 18" from p-trap... this is NOT what the code says, but is that what it means to say?

    OR to put it another way...
    Q3+: what is the recommended height above the floor for the top of the standpipe? Should it be above the flood level of the washer (as I've seen mentioned in one resource)? Can it be "hidden" behind the machine (for aesthetics) or does it need/want to be above the machine?

    Thanks.

  2. #2
    One who lurks Basement_Lurker's Avatar
    Join Date
    Jun 2007
    Location
    Victoria, BC
    Posts
    668

    Default

    If you search, this has probably already been answered several times by now.

    804.1 All plumbing fixtures or other receptors
    receiving the discharge of indirect waste pipes shall be
    approved for the use proposed and shall be of such
    shape and capacity as to prevent splashing or flooding
    and shall be located where they are readily accessible
    for inspection and cleaning. No standpipe receptor for
    any clothes washer shall extend more than thirty (30)
    inches (762 mm), nor less than eighteen (18) inches
    (457 mm) above its trap. No trap for any clothes
    washer standpipe receptor shall be installed below the
    floor, but shall be roughed in not less than six (6)
    inches (152 mm) and not more than eighteen (18)
    inches (457 mm) above the floor.

    The top of the standpipe MUST be above the FLR of the appliance no matter what, and it sounds like your code wants a minimum dimension of 18", and a maximum dimension of 30", for the standpipe dimension. That's more than enough information to figure out what you have to do.
    Broken promises don't upset me. I just think, why did they believe me? -Jack Handy


    www.blackbirdkitchenandbath.com

  3. #3
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    It definitely needs to extend above the water level of the machine or it will gravity drain the machine.
    The discharge on most machines is pumped without a valve.

    A trap set 6" above the floor with an 18" standpipe while legal would be a problem for most machines.
    Last edited by Redwood; 12-22-2010 at 03:56 PM.

  4. #4
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    All of the machines I am familiar with have a control panel on the back that extends above the level of the tub. This would allow the standpipe to extend above the top of the tub and still be hidden. That would put the height somewhere around 36". I hope you know the drain is supposed to be 2" pipe. In years past, 1-1/2" was enough, but new machines empty the water much faster than a 1-1/2" pipe can accommodate.

  5. #5
    DIY Senior Member DavidTu's Avatar
    Join Date
    Dec 2009
    Location
    Seattle, WA
    Posts
    229

    Default

    OK thanks, the FLR is the key determinant then for the overall height. Yes I am running 2" pipe. BUT no one has indicated what the point of reference is for the p-trap height to be measured as being 6" above the floor... what part of the p-trap must be > 6" from floor?

  6. #6
    George the Plumber Gsalet's Avatar
    Join Date
    Sep 2010
    Location
    San Francisco
    Posts
    83

    Default

    I believe the code states the trap must be no less than 6" or greater than 18 to the weir of the trap.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,659

    Default

    I put the trap somewhere between 6" and 18", and the standpipe at 42". That puts the box at a point where the valves are accessible, in case the homeowner is one of those "three people in America" who acutally turn the valves off after every wash.

    Your "less than/greater than" statements are slightly incorrect. It should be 6" <= P trap <= 18" and 18" <=standpipe <= 30"
    Last edited by hj; 12-23-2010 at 07:05 AM.

  8. #8
    One who lurks Basement_Lurker's Avatar
    Join Date
    Jun 2007
    Location
    Victoria, BC
    Posts
    668

    Default

    I also put the standpipe/washbox at 42".
    Broken promises don't upset me. I just think, why did they believe me? -Jack Handy


    www.blackbirdkitchenandbath.com

  9. #9
    DIY Junior Member jaginc's Avatar
    Join Date
    Dec 2012
    Location
    Oregon
    Posts
    1

    Default Thanks for the accurate info.

    I know this thread is a bit old and you may never read this, but thanks so much for actually quoting and referencing the applicable code. I spent several frustrating hours searching various forums and threads, finding lots of statements, but no code references to back them up. I am trying to figure out how to plumb in a washing machine in a daylight basement which is part of a large addition/remodel to my house. Originally the laundry was to be on the other side of the wall on the main level and the plumbing would have been easy, but we decided to move the laundry to the basement part way through the project. Unfortunately we are a few inches too low to put the trap in the wall easily. At least now that I am able to find the exact requirement in the 2011 Oregon Plumbing specialty code, I know the exact limitations I have to work around.

    Quote Originally Posted by Basement_Lurker View Post
    If you search, this has probably already been answered several times by now.

    804.1 All plumbing fixtures or other receptors
    receiving the discharge of indirect waste pipes shall be
    approved for the use proposed and shall be of such
    shape and capacity as to prevent splashing or flooding
    and shall be located where they are readily accessible
    for inspection and cleaning. No standpipe receptor for
    any clothes washer shall extend more than thirty (30)
    inches (762 mm), nor less than eighteen (18) inches
    (457 mm) above its trap. No trap for any clothes
    washer standpipe receptor shall be installed below the
    floor, but shall be roughed in not less than six (6)
    inches (152 mm) and not more than eighteen (18)
    inches (457 mm) above the floor.

    The top of the standpipe MUST be above the FLR of the appliance no matter what, and it sounds like your code wants a minimum dimension of 18", and a maximum dimension of 30", for the standpipe dimension. That's more than enough information to figure out what you have to do.

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,659

    Default

    quote; I know this thread is a bit old

    I was wondering why every posting prior to yours was dated 2010, and yours was "yesterday". I thought maybe the website was broken and misdating the posts.
    Licensed residential and commercial plumber

Similar Threads

  1. Minimum Trap Arm?
    By dlarrivee in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 02-06-2010, 10:03 PM
  2. Trap arm height, minimum tail piece length
    By davefoc in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-18-2009, 09:20 AM
  3. Highest height on comfort height toilet
    By BOB J in forum Toilet Forum discussions
    Replies: 3
    Last Post: 03-05-2009, 12:43 PM
  4. Laundry Tray Drain into Standpipe?
    By kkunze in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-21-2009, 08:44 AM
  5. Standard height vs. comfort height
    By Cygarbuff in forum Toilet Forum discussions
    Replies: 2
    Last Post: 11-12-2004, 08:35 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •