Thread: Would There Be A Fire?

  1. #1
    DIY Senior Member molo's Avatar
    Join Date
    Sep 2006
    Location
    cold new york
    Posts
    840

    Default Would There Be A Fire?

    My question is about an electric oven. The outlet is a 3-prong 220 outlet with a fuse (not a circuit breaker). The cord was missing on the stove. I accidentally grabbed a 10 ga. 30amp electric dryer cord (which wouldn't have plugged into the outlet). If it had been able to plug in would the fuse have prevented a fire or would the cord have started to smoke/burn?

    Thanks,
    Molo
    "Any American who is prepared to run for President should automatically, by definition, be disqualified from ever doing so."
    Gore Vidal.

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    That cord is designed to safely handle 30 amps. A stove may draw 40-ish amps, and might be fused for 40 or 50 amps. SO, the fuse does not protect the cord from being overloaded. In the scenario you describe, we do not jump right to "fire"...but the insulation might get too warm, could even melt, and eventually bad things could happen. The different PLUGS are "different" for this exact reason...so you can't plug into the wrong place!

  3. #3

    Default

    If it had been able to plug in would the fuse have prevented a fire or would the cord have started to smoke/burn?

    A proper fuse would prevent an overload.

    In normal operating condirions, the #10 cord wouldn't even come close to overheating.


    That said, a fire can still happen, even with all the proper things in place. The right kind of short circuit, especially on a 50 amp breaker, can do some real damage before it trips.

Similar Threads

  1. Fire damage
    By Bill Arden in forum Remodel Forum & Blog
    Replies: 16
    Last Post: 06-01-2009, 09:31 PM
  2. House Fire Sprinkler
    By Master Brian in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 16
    Last Post: 11-20-2008, 01:43 PM
  3. Fire Hose Coupling
    By sjsmithjr in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 09-26-2008, 11:59 AM
  4. Dryer vent fire
    By Southern Man in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 09-16-2008, 11:14 AM
  5. Playing with fire??
    By fast pasquale in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 02-10-2007, 07:40 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •