    Help! My one-year old Takagi Jr used in a radiant heat installation has died. It worked fine last winter and seemed to be Ok this year until we got some below 0 weather. If I turn off elec., wait a minute, then restart, it will fire and everything seems normal. It will run about 1-2 minutes, then quits and shows error codes. Error codes seem to alternate between light flashing 3 times and light flashing 4 times. I've cleaned the flame sensor as mentioned in another post (and damaged the fiber gasket but I think i pieced it back together OK). The only difference between this year and last is that I added a direct vent. I bypassed the direct vent (opened the cover on the unit) and then the unit ran until the thermostat shut it off but now it will not run again. I should also mention that the exhaust vent is dirty with what looks like soot. Hope this is not too confusing and someone has some ideas - No one in my area seems to work on these units.

  2. #2
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Check for obstructions (including frost) on the air-intake venting for starters.

    Is this a propane or gas unit (and is it on the correct fuel?).

    Call the Takagi technical help line- they have a reputation for being able to talk most anyone through a debugging cycle.

  3. #3
    DIY Junior Member
    Join Date
    Dec 2010
    Location
    Wisconsin
    Posts
    2

    Default

    Thanks for your ideas - Both intake and exhaust are clear. This unit runs on LP and the dip switch is correctly set for LP. I will try Takagi tech support.

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    IIRC, the dip switch only indicates to the control board which coefficients to use in order to have the same control board for both the -LP and -NG models. If the model number ends in -NG you have it running the wrong fuel (it'll usually run, but with the wrong mixture, and neither it's longevity nor it's efficiency will be near expectations.)

    In cold weather frost formation on air intakes can make burners run fuel-rich, and can show up as sooty deposits before it out & out won't run.

    According to the manual (see p.17) a 3-blink error code can mean issues detected with any of :

    Hi-limit
    Igniter
    Flame Sensor
    Main Gas Valve
    Proportional Gas Valve
    Abnormal Burning

    A 4-blink can mean issues with either:

    Fan
    Pressure switch

  5. #5
    DIY Junior Member Tecno's Avatar
    Join Date
    Dec 2010
    Location
    maine
    Posts
    2

    Default

    Do you have a Backflow preventer installed in the Exhaust pipe?? if so make sure that it can move freely.I have one on my unit and i found that it had stuck shut my bad should have done the yearly check on the unit I cleaned out the pipe and made sure that it moved freely and it fixed the problem.

Similar Threads

  1. Over Under Radiant Heat?
    By Uhhh...Clem! in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 11-20-2009, 07:55 AM
  2. radiant heat question
    By donk in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 10-18-2009, 07:48 AM
  3. Problem with Takagi & Radiant Heat &Domestic Hot Water
    By siammurph in forum Tankless Water Heater Forum
    Replies: 21
    Last Post: 09-29-2009, 01:29 PM
  4. Problem with Takagi & Radiant Heat &Domestic Hot Water
    By siammurph in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 12-20-2008, 12:24 PM
  5. more radiant heat questions.
    By Randyj in forum Remodel Forum & Blog
    Replies: 19
    Last Post: 02-19-2007, 04:01 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •