Boiler not operating within Hi Lo limits

Users who are viewing this thread

ut7351a

New Member
Messages
2
Reaction score
0
Points
0
Location
PA
I have a Teledyne Laars Max D100 Boiler w/ indirect hot water. It is a cold start boller. It has separate Hi Lo limit controls. Hi limit set at 200F, Lo limit set at 180F. Problem: When thermostat calls or heat, boiler heats up to about 165F & burner cuts out. As water circulates boiler temp starts to drop. When boiler temp drops to about 155F, burner kicks back in & heats up to about 165F again & continues back & forth until thermostat is statisfied. Why isn't boiler operating between the Hi Lo control settings?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Does it have an outdoor reset controller? If so, it adjusts to the load and outside temperature and overrides the manual settings.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
This boiler probably has a safety high-limit aquastat in addition to the operational high/low settings. If the safety is set (or has failed) to 165F (lower than the operational high limit) it would exhibit this sort of behavior- kick off at 165F, back on again at 155F, repeat...

Is this the boiler in question?

If it's this series or similar and you incorrectly assumed the safety aquastat to be the low-limit, that could be the whole issue. (although 165F is way lower than the 180F you set it to.)

What model aquastat(s) does this beast have?
 