    Default Boiler not operating within Hi Lo limits

    I have a Teledyne Laars Max D100 Boiler w/ indirect hot water. It is a cold start boller. It has separate Hi Lo limit controls. Hi limit set at 200F, Lo limit set at 180F. Problem: When thermostat calls or heat, boiler heats up to about 165F & burner cuts out. As water circulates boiler temp starts to drop. When boiler temp drops to about 155F, burner kicks back in & heats up to about 165F again & continues back & forth until thermostat is statisfied. Why isn't boiler operating between the Hi Lo control settings?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    Does it have an outdoor reset controller? If so, it adjusts to the load and outside temperature and overrides the manual settings.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member ut7351a's Avatar
    Join Date
    Dec 2010
    Location
    PA
    Posts
    2

    Default

    No Outdoor controller.

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,713

    Default

    This boiler probably has a safety high-limit aquastat in addition to the operational high/low settings. If the safety is set (or has failed) to 165F (lower than the operational high limit) it would exhibit this sort of behavior- kick off at 165F, back on again at 155F, repeat...

    Is this the boiler in question?

    If it's this series or similar and you incorrectly assumed the safety aquastat to be the low-limit, that could be the whole issue. (although 165F is way lower than the 180F you set it to.)

    What model aquastat(s) does this beast have?

Similar Threads

  1. Boiler operating pressure
    By rockycmt in forum HVAC Heating & Cooling
    Replies: 7
    Last Post: 11-29-2010, 05:52 AM
  2. What is better operating system?
    By alleonna in forum Computers and Stuff
    Replies: 18
    Last Post: 10-04-2006, 09:46 PM
  3. Dual operating system.. is it okey?
    By alleonna in forum Computers and Stuff
    Replies: 2
    Last Post: 07-09-2006, 06:24 PM
  4. Broken Woodford operating rod
    By Woody in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 06-26-2006, 08:24 AM
  5. Advice on height limits of Washing Machine disposal pipe
    By barryhepburn in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 05-29-2006, 04:52 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •