LG Mini-Split Heatpump system - Operating temp?

Users who are viewing this thread

yds

New Member
Messages
10
Reaction score
0
Points
0
Location
Toronto, Ontario
I have an LG minisplit ductless system installed in my new third floor addition here in Toronto (outdoor unit model LMO240H; indoor units LMI090HP). The contractor who installed it said it should operate up to about -15C outside temp. We're currently at about -5C, and I'm not getting a lot of heat out of either head-unit (there are two). Should I be? What the the typical operating ranges for this (or similar) ductless heatpumps??
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
You need to look at the specs for the unit. -5C is reasonable, -15C is surely pushing the limit. When you use a heat pump in such a cold climate, it is common to have secondary electric strip heat, to "jump start" the heat in the room. The mini-splits do not have that. Under the best of circumstances, a heat pump does hot produce hot air, it produces air just several degrees warmer than the current room air. Left on long enough, it will raise room temp, but it may take a while.


I looked at the website, did not see your model number exactly, but the newer inverter heat pumps do reference a range down to 5ºF, which is your
-15ºC. At these low temps, you will feel just a slightly warmish breeze coming from the air handler!
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
My father had a heatpump system in upstate NY - the town where he lived had a local electrical co-op, and the rates were cheap by comparison. I wouldn't put that system in my home, but I guess they got used to it (would consider it if the winter temps weren't so cold, though, or the rates here were more conducive to it). I never really liked it since the air temp out of the vents was barely warm. His system did not have an easily changed fan speed, so you also had the wind chill effect since the fan was optimized for a/c, not heat. As the outside air temp drops, there's less and less heat easily available, and the output temp drops even more. Without backup heaters, there will be times during the winter in Toronto where they may not produce much of any heat.
 

yds

New Member
Messages
10
Reaction score
0
Points
0
Location
Toronto, Ontario
Without backup heaters, there will be times during the winter in Toronto where they may not produce much of any heat.

We do have baseboard electrics as a backup - I knew I wasn't going to get away with going the entire winter with just the heatpump. But we're only barely below the freezing mark at this point in the season and I was hoping to get nice warm air out of the LG for a bit yet.

As a side note, the LG wall units have a "chaos" air feature which alternates the fan speed as well as oscillating the vent direction vertically and horizontally. Works pretty well in evenly distributing the heating/cooling around each room (the two rooms we have the head units in are each only about 175sqft).
 

yds

New Member
Messages
10
Reaction score
0
Points
0
Location
Toronto, Ontario
I had sent a note off to LG customer care about he operating temps. Here is their response:

Hello, thank you for contacting LG Customer service.

The minimum temperature the heat pump can be used is -5C using the unit any colder than this temperature can damage the unit.

Thanks
Dave H.
LG Customer Service
LG Canada


HMMMM. Not exactly what my contractor told me, but consistent with what seemed to be happening. Just curious - how would use below the recommended temp cause damage? Would/could it burn out the compressor?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The internal logic (should) prevent it from operating when it gets that cold. Compressors are designed to compress gas to fluid...if it is really cold, the fluid may not evaporate, and it would be liquid coming back in. Can't compress liquid, and the high pressure cutout may trip. Note, I'm not a pro on this... Ideally, there should be a temperature sensor that would prevent the compressor from turning on before the point damage could occur.
 