I live in Virginia. The temp is around 45F. I have Ducane heat pump outside. it is not running at all but the inside furnace fan is working well. I just changed the defrost circuit board since the HVAC service guy said the old one needed to be replaced. The thermostat seems in good condition because i just got a new Honeywell 5-1-1 programming one and works well. So far, the defrost circuit board and thermostat are all brand new. What is the problem to cause the heat pump not running? I pressed the valve button on the heat pump which can make it run. But it stops if i release the press. Is there possible to be the circuit board wiring problem?

Any advice is appreciated. :p it is so cold here.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Sounds sort of like you had a refrigerant leak, and the system is low, causing a lockout. This is likely something a service tech might need to look at. If the reverse switch valve is not working, it can't make heat. Don't know enough about a heat pump to help more. Does the thermostat have a setup so it can control a heat pump? Is it hooked up properly? There may be a dip switch or jumper that needs to be moved. Carefully read the installation instructions again and make sure you use the section on a heat pump to verify it is wired properly.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Not all thermostats are compatible with heat pumps, so that MIGHT be a factor. I am not sure what that button does, so cannot comment on whether it is bypassing some safety circuit, or not being energized by the air handler or thermostat.
 

Henry Lee

New Member
Messages
3
Reaction score
0
Points
0
Location
Alexandria, VA
thanks for your reply.

Thanks for the reply from jadashua.

The heat pump is not running at all but the inside furnace fan works and gets some heat. I just changed the defrost circuit board since the HVAC service guy said the old one needed to be replaced. Freon level is ok. I pressed the button (contactor) on the heat pump and it ran. But it stops running if i stop pressing the contactor. So you think i need go back to recheck the thermostat wiring?
 

Henry Lee

New Member
Messages
3
Reaction score
0
Points
0
Location
Alexandria, VA
I bought the brand new Honeywell TH6320U1000 5-1-1 Programmable Thermostat. It works for heat pump. The HVAC service guy came and set the thermostat and air handler wiring. He said if i got the new circuit board and get it replaced. It should
work. But it didn't work as the guy told me.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
On as thermostat like your new one, you have to go through the set-up program and set up the O/B function. That is, there is a terminal which will signal the outside reversing valve. That terminal may be set to send 24 volts on a call for HEAT, or a call for COOL. It probably defaults to call for cool. You need to find out on -your heat pump which way the reversing valve works, and then program the T-stat accordingly.


But....if the outdoor unit does not turn on at all ( fan running? compressor running?) then it is a problem besides the reversing valve.
 
Last edited:

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
Love those guys that change parts as a method of troubleshooting.

If its too cold, seems the pump would shut down and call for the heat strips to cut in. Maybe the strips do not work?
 

jseger

New Member
Messages
1
Reaction score
0
Points
0
Location
Alexandria, VA
Henry,

Did you ever figure out what the problem was with your heat pump? I live in VA as well and have the exact same issue. HVAC technician came in and said the wall thermostat was bad. He installed a new Honeywell thermostat but the heat pump still would not work. Then the technician said the Defrost Control board on the heat pump was bad. That was replaced with a new one and the heat pump still does not work.

If I manually press the contactor on the heat pump, it comes on. So it does not seem to be the contactor or compressor. I double checked the thermostat connections and settings and they are exactly as prescribed in the instructions. Next step might be to put the old thermostat back and see if that works.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Sometimes, the installer may not follow the recommended color code on the wiring, and if you blindly install a new thermostat without carefully marking the old one's wire positions, it will never work. So, check out the air handler side to ensure that the wires are on the 'proper' places, then check the thermostat again. Ideally, it should be just a straight-through red-red, yellow-yellow, etc...but if someone was sloppy???
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks