    Default Convert Mobile Home to Central Air; Have Central Heat

    What size outdoor compressor should I get for a 14' x 66' MH? I already have central heat. I have always heard the rule is 1 ton of unit for every 600 sf. of heated and cooled living space. I will need to get an "A" coil also. Anything to consider with that?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,401

    Default

    Rule of thumb can be quite expensive! You need to do a manual-j heat load analysis. If you do a search, you can probably find a free calculator, or have the vendor do it for you. It depends on the insulation, windows, orientation, and local ambient conditions. AL can be quite hot and humid. To remove the humidity means if the a/c is too large, it won't run long enough to pull the moisture out of the air and you'll be cold and clammy. You're better off with one slightly small verses one too big as you'll be more comfortable at a higher temp if the humidity is low, verses cold, but clammy.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    It is tough to do a rough guess on a mobile home, because your construction and insulation are different, possibly minimal. How many BTU is your furnace? I am guessing it may be relatively small, in your climate. You will have to determine from the manual for that heater how many tons of A/C the blower will support. But since you are well under the 3 ton range, it is likely that will not be a problem. A local HVAC guy should be able to figure this out.

    Yes, you need a cased coil attached to the furnace. Is there room on top of the furnace for that, where it sits?

    Around here, you could get the coil and a 1 T R410 condensing unit , installed, between $3k and $4k.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    An area enclosed by glass will need a much LARGER heating/cooling unit, than one completely enclosed with well insulated walls. The size unit you need will depend on your window areas, the orientation of you mobile home, the insulation in the walls, floor, and ceiling (probably minimal). Too small and it will run continuously. Too large and it will not run often enough to provide the needed dehumidifying in the area.

  5. #5
    Retired prof. engr. gator37's Avatar
    Join Date
    Nov 2009
    Location
    Alabama
    Posts
    108

    Default

    jadnashua is correct about sizing

    but if you get an estimate on a condenser, refrigerant lines, A coil and electric to your condenser plus a new heat/cool T-stat, you might want to consider a package unit, gas heating electric cooling with either propane or natural gas what ever is available in your neighborhood . Then you can remove the furnace, patch the duct, and have closet space for shelves or something useful. They could run metal round to the center of the existing air supply line add a return grill w/ return duct in you living room and insulate the duct with foil back wrap under the mobile home.
    By the way I live just outside of Huntsville in Madison County.

Similar Threads

  1. Central Air Questions for Old Home
    By bjferri in forum HVAC Heating & Cooling
    Replies: 13
    Last Post: 06-29-2009, 01:11 PM
  2. Central Vac Plumbing
    By BrianPlumBrian in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 12-01-2008, 06:12 AM
  3. About to get a new central unit.....
    By SD44 in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 05-12-2008, 08:05 AM
  4. central heat/air install--product selection
    By homey6660 in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 11-05-2007, 05:11 PM
  5. Extending Central Heat to 2nd and 3rd Floors
    By colden in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 11-25-2006, 08:46 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •