    Default Combustion order from water heater fan

    This seems to happen only during the winter time. The vent on top of the WH has a somewhat open back side and I can feel a draft coming out of this opening instead of up through the vent pipe and my basement fills with a strong combustion odor. Now if I open my glass sliding door in the basement, the air then goes out the vent and the smell disappears. Any advice? Could it have something to do with my furnace air flow since this only happens in the winter? My furnace is only a few feet from the WH. My basement is a very open environment, also. Thanks for any help.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,395

    Default

    Combustion devices actually can suck a lot of conditioned air out of a house. In the process, they suck unconditioned air in the house. The newer devices use closed combustion, where the burner gets all of its combustion air from outside, and then dumps the exhaust there as well. So, basically, combustion devices rely on sucking air in from outside to burn properly. It's better to do this in a controlled manner rather than have it do it through all of the cracks in the house. If the house is tight, it becomes worse, the device won't work right. By that, one possibility is incomplete venting - dumping it in the house rather than outside. Or, if there's not enough air, make some CO rather than CO2, which could kill you. If you don't have one, suggest you get yourself a CO detector and use it. You may need to provide an outside air vent to the area where the burners are.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by paulcat View Post
    This seems to happen only during the winter time.
    I can feel a draft coming out of this opening instead of up through the vent pipe and my basement fills with a strong combustion odor. Now if I open my glass sliding door in the basement, the air then goes out the vent and the smell disappears.
    Probably 'cause cold air sinks. You may need a draft inducer. Also, with 3 CO detectors you'll have aircraft reliability, 99.9999%, the so-called "six-nines".

    Some of your brain cells have already died if you smell that odor or if your eyes smart. With nausea and headaches, flu-like symptoms, you are close to dying. One of my customers had that, and survived.

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    Flues open to the basement would normally put the basement under negative pressure from the "stack effect". Opening the slider allows outdoor air in to relieve that pressure differential, and the air/combustion exhaust to flow up the flues as-designed. But if there are other induced- exhaust points (kitchen/bath fans, or clothes dryers), it can create sufficiently negative pressure when the slider is closed that air comes down the flues, a condition called "backdrafting".

    Backdrafting combustion appliances are a serious health hazard- take this deadly-seriously!

    If there is a powered draft-inducer on the furnace it may be THE problem (and not the usual backdrafting) since the forced draft of the furnace would pressurize the flue forcing some of it's exhaust into the basement. If the furnace is atmospherically drafted, adding power draft inducer just on just the hot water heater could create reversed draft problem at the furnace whenever the hot water heater is running.

    Is the furnace a forced-draft version?

    Almost all 83%+ furnaces & boilers are induced draft, and should never share a flue with an atmospheric-drafted hot water heater. Do the furnace & hot water heater share a flue, or are they on separate flues?

    If they're both atmospheric-drafted and share a flue, sometimes adding 4-5' to the top of the chimney is enough. Alternatively, a turbine-vent or venturi-vent chimney cap can often do the trick.

    Sometimes the flue has too large a bore for the BTU rating(s) of the burner(s) attached, and would draft better with a narrower-bore liner installed.

    Properly diagnosing the cause may lead to different "right" solutions depending on the particulars.

Similar Threads

  1. Can I Draw Exterior Combustion Air In For My PowerVent Water Heater?
    By ahadave in forum Water Heater Forum, Tanks
    Replies: 3
    Last Post: 01-23-2010, 05:25 PM
  2. Adding combustion air
    By Lakee911 in forum HVAC Heating & Cooling
    Replies: 11
    Last Post: 11-03-2009, 04:17 PM
  3. Combustion Tests
    By flwriting in forum Boiler Forum
    Replies: 13
    Last Post: 09-08-2009, 06:33 AM
  4. Combustion Air intake?
    By smartin684 in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 01-05-2009, 07:08 PM
  5. Oxygen to Sealed Combustion Hot Water Tank
    By molo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 10-11-2007, 02:11 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •