    Default Heat Pump Short Cycling to Hold Temp.

    Hi all, I have a roof mounted heat pump that when in the heat mode it appears to cycle normally until it reaches the set temp on the t-stat, then it really short cycles to hold the temp.

    Once it reached the set temp it will cycle on for about 6 minutes and then off for only 3-4 minutes before cycling on again. If i increase the t-stat a couple degrees warmer it appears to cycle as it should until it reaches the new desired temp. I suspect it's t-stat related but plan to call my AC guy out to take a look. Just curious if there is anything obvious that would be causing this ? It does not let it drop a single degree before cycling on... shouldn't there be a degree or 2 fluctuation?

    T-stat is a Honeywell IV.

    One other item, it appears to defrost more than it should - 2-3 times during the morning after I turn it on to warm the house up.


    Any insight? This is my first winter in this house.
    Last edited by Phillbo; 11-29-2010 at 08:58 AM.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,446

    Default

    SOme thermostats have the ability to program them for the type of heat you are using...ensure if yours does that it is set to indicate it is controlling a heatpump. Some can also enable you to set the hysterisis of the heat control (i.e., to let it swing more). If the house is cooling off enough in 3-5 minutes to trigger the thermostat, you need to find the air leaks and maybe beef up the insulation, though, unless it is sitting in a drafty area. Placement of the thermostat can sometimes be critical.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Member Phillbo's Avatar
    Join Date
    Nov 2008
    Location
    Arizona
    Posts
    77

    Default

    It does not cool off in the 3-5 minutes between cycles.. I can decrease the temp setting a couple degrees and it takes a long time ( almost a couple hours ) to drop enough for the unit to cycle on again. The house is older but has great insulation, teh temp does not even need to drop (according to the t-stat reading ) for the unit to cycle back on.

    I find myself having to manage the t-stat.. turn it up to 2* higher than I want and when it passes the desired temp, set it for 1* below what I want... otherwise it short cycles and does not increase the temp of the house at all.

  4. #4
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    It almost has to be the hysteresis adjustment.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,446

    Default

    The electronics can detect much smaller temperature differences than a whole degree, so depending on how it is set, it is trying to maintain as close to the set point as possible. If you tell it it is a heat pump (and not say the strip heaters), it should be less aggressive in trying to maintain exactly the setpoint.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    DIY Member Phillbo's Avatar
    Join Date
    Nov 2008
    Location
    Arizona
    Posts
    77

    Default

    Quote Originally Posted by jadnashua View Post
    If you tell it it is a heat pump (and not say the strip heaters), it should be less aggressive in trying to maintain exactly the setpoint.
    OK. I walked up to it and said " you are a heat pump" and it ignored me


    How do i set it to "heat pump" ? Do I need to take the face off like I was changing the batteries?
    Last edited by Phillbo; 11-29-2010 at 05:00 PM.

  7. #7
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,730

    Default

    Quote Originally Posted by Phillbo View Post
    OK. I walked up to it and said " you are a heat pump" and it ignored me


    How do i set it to "heat pump" ? Do I need to take the face off like I was changing the batteries?
    Which EXACT model is the thermostat? Is it from the Honeywell Chronotherm- IV series? If yes, it already knows it's a heat pump, and has a programmable hysteresis. Some variants had a "learning" function to limit overshoots & short cycling as well. Dig up the manual (it might be online, might not.)

Similar Threads

  1. Shallow Well Pump - Constant Short Cycling with Irrigation System
    By Gheuett in forum Pumps and Tanks Well Forum & Blog
    Replies: 7
    Last Post: 09-22-2010, 05:43 PM
  2. Tank Pressure at Zero, Pump Short Cycling
    By woodworkergal in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 12-28-2009, 12:58 AM
  3. Pump is short cycling.....Very short!!
    By crittercatcher in forum Pumps and Tanks Well Forum & Blog
    Replies: 17
    Last Post: 06-29-2009, 09:26 AM
  4. Short Cycling Pump - Confused
    By tracyandskye in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 11-07-2008, 06:54 AM
  5. Irrigation pump short cycling overheating...GGRGGR
    By tombong in forum Irrigation / Sprinkler Forum
    Replies: 4
    Last Post: 06-15-2008, 07:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •