Thread: How does this Basic Washer Set-Up look?

  1. #1
    DIY Junior Member turnerAK's Avatar
    Join Date
    Nov 2010
    Location
    Alaska
    Posts
    5

    Default How does this Basic Washer Set-Up look?

    I'm getting my plumbing feet wet with a laundry room remodel. I have the pipes assembled in this picture but not glued yet. The left T is a 1 1/2" vent which ties into a 2" vent in the ceiling. The 3" down is the start of a stack that will have a master bath added to it from upstairs. I had to extend the length of my drop pipe from 8" to 24" as I noticed code says 18" minimum. Thanks for your feedback!

    Happy Thanksgiving to all!


  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    2" p-trap and trap arm.
    1-1/2" vent, which on the horizontal should be vented with a combo fitting, not a Santee.
    You may want to pick up some hammer arrestors for the washer. They can thread onto the back of the machine and then the hoses attach to them.

    Your inspector may allow the santee in that position, they don't in Washington State.
    What part of Alaska?

    Here is a combo, not turned the right way for your job though.

    Last edited by Terry; 11-25-2010 at 11:28 AM.

  3. #3
    DIY Junior Member turnerAK's Avatar
    Join Date
    Nov 2010
    Location
    Alaska
    Posts
    5

    Default

    Thanks Terry. I guess I'm not familiar with the term 'combo fitting' and I chose the sweeping Santee to provide enhanced air flow. I'll look into the 'combo'. Also, I read that the flexability of PEX eliminates water hammer. Is this counter to what you've experienced? I'll look into the device you recommend, thanks for the advice!

    I'm in Anchorage now, via Spokane last summer.

    PS: Thank you for this forum! You may remember my post regarding a sub-grade shower drain that was installed without a p-trap based on bad advice. As a result of the feedback received on here, my contractor and I wll be opening the floor back up and finding a way to fit the p-trap and proper vent into the space.
    Happy Thanksgiving!

    Last edited by Terry; 11-25-2010 at 11:28 AM.

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    A combo is a single fitting which replicates a WYE with a 45 ell coming off. In general terms, it is a broader sweep than the santee. The code all has to do with the likeihood of clogging the vent with waste from the pipe. A santee is used to send waste horizontally, into a vertical pipe. As terry said, some codes will accept that santee in your vent situation, some codes require all vent fittings below the flood rim to be "vent" configuration rather than "drainage" configuration.

    It is not a big deal at all, UNLESS you have an inspector who rejects it!

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    On PVC pipe, the socket to pipe joint is an interference fit...IOW, you can't bottom the pipe out in there until you apply the cement which literally melts the top layer and the pipe can then be pushed to the bottom. I don't know if ABS works the same way. If it does, you'll find you are short, since dry fitting it means, even if you have it 'tight', it is not bottomed, and it will be when you add the cement. This can be a major pain, as each joint adds more to the overall length deficit. the only reliable way to do this is to actually measure and then cut, not try to assemble then measure on dry fittings.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Yes, ABS is also built as interference fit

  7. #7
    Network Engineer rmelo99's Avatar
    Join Date
    Jul 2006
    Location
    Connecticut
    Posts
    349

    Default

    Isn't that a combo over there on the right going into your 3" stack?

    I never was able to find combos @ the Depot so always resorted to "making" them with a WYE and a 45deg street elbow. I then found them at lowes, it's cheaper than making it with 2 pieces.

    Like Terry said it all depends where you are. I think for venting (as your using) in my locale it is permitted, just not for drainage. There have been many a thread about Santees on their back. You can't go wrong with what has already been recommended to you.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    quote; As terry said, some codes will accept that santee in your vent situation, some codes require all vent fittings below the flood rim to be "vent" configuration rather than "drainage" configuration.

    You have it reversed. Most codes call for ALL fittings below the overflow level to be "drainage" style NOT vent type. As long as there is a vent between the trap and the vertical connection, the connection to the vertical pipe can be either a sanitary tee or a combo. If there were no vent, then it would HAVE to be a sanitary tee.

  9. #9
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Yes I got those backwards.....I am blaming the turkey. That's my story and I am sticking to it!!!!!!

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    Yeah, blame the turkey, now that he is not around to defend himself.

Similar Threads

  1. Proximity of washer & dryer outlets to washer valves & tub?
    By Plumbob in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 12-18-2009, 01:44 AM
  2. basic questions
    By eod4647 in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 07-27-2009, 06:29 PM
  3. switching 15-amp to 20-amp (basic Q's)
    By BrownShirt228 in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 09-28-2008, 11:25 AM
  4. Basic lav rough in
    By santhony7 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-11-2007, 11:53 AM
  5. basic question
    By kathy carr in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 10-22-2005, 02:18 PM