    I have a 50amp 220v line (3 wire plus ground) in my master bath that is hard-wired to a hot tub. Remodeling the bathroom and replacing the hot tub with a 110v air bath. Can I use the 220v line to feed a sub-panel (I would hide it in a closet in the bathroom) and then branch two 110v circuits out of the sub-panel?

  2. #2
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Post a link to the specs for your hot tub.

  3. #3
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    It's 18 years old, I can't even find it on the manufacturers website.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by StatManLV View Post
    I have a 50amp 220v line (3 wire plus ground) in my master bath that is hard-wired to a hot tub. Remodeling the bathroom and replacing the hot tub with a 110v air bath. Can I use the 220v line to feed a sub-panel (I would hide it in a closet in the bathroom) and then branch two 110v circuits out of the sub-panel?
    NO

    You can not put a panel in the bathroom or in a closet.

    Yes you can use the branch circuit to feed a panel as long as the conductors are protect at or below the ampacity of the conductors.
    The panel can not face in the bathroom or a closet but can be in the same wall as long as it faces out of these places.

  5. #5
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    Quote Originally Posted by jwelectric View Post
    NO

    You can not put a panel in the bathroom or in a closet.

    Yes you can use the branch circuit to feed a panel as long as the conductors are protect at or below the ampacity of the conductors.
    The panel can not face in the bathroom or a closet but can be in the same wall as long as it faces out of these places.
    Can you explain why it can't be in the bathroom closet?

  6. #6
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    It is an electrical code issue (NEC). Panels are not allowed in closets or bathrooms.

  7. #7
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    Bummer, thanks for the clarification. Guess I need to go to plan B

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by StatManLV View Post
    Can you explain why it can't be in the bathroom closet?
    Well in a closet we have all kinds of stuff like cloth that will burn real easy. In the bathroom we have a lot of moisture in the form of a vapor such as steam and other things like this.

    Besides all this it is a violation of 240.24(D)&(E) of the NEC. (D) says no overcurrent devices in a closet and (E) says no overcurrent in a bathroom. Now if you wanted to set a panel in either location it would be okay just as long as you didn't install any overcurrent devices such as fuses or breakers.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    I think you would need to run another cable. While neutral is connected to ground in the main panel, a subpanel needs the neutral and ground to be separate, along with the two legs (i.e. a 4-wire cable, not three). The neutral is supposed to carry the return current, not the ground wire. The ground is for safety, not current for normal operation. A 240vac device does not need the neutral lead, but a 120vac circuit does.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    Quote Originally Posted by jadnashua View Post
    I think you would need to run another cable. While neutral is connected to ground in the main panel, a subpanel needs the neutral and ground to be separate, along with the two legs (i.e. a 4-wire cable, not three). The neutral is supposed to carry the return current, not the ground wire. The ground is for safety, not current for normal operation. A 240vac device does not need the neutral lead, but a 120vac circuit does.
    The current cable is a 4 wire cable.

  11. #11
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    Seen MANY panels in closets. Never saw a fire. They get a lot less water vapor than the feeder panel outside on the pole or wall. Those code panels exposed in a hall usually get a picture hung over them so they cant be located anyway.

    By the way, you already have at least one 120v circuit by using that big cable and one of the hot wires. Get rid of the 50 amp breaker and feed one wire with a 20 amp breaker at the main panel. Put a J box in the bath and hook up your 12g romex to that one wire and the ground and neutral.

    You also have the second 120v circuit by duplicating that with another 20 amp breaker at the panel and sharing the neutral, but the guys here will probably scream.

    PS: why [2] 120 v circuits for a bathtub air blower? You would also need GFCI breakers unless the tub has its own.

  12. #12
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    Quote Originally Posted by ballvalve View Post
    PS: why [2] 120 v circuits for a bathtub air blower?
    One for the blower and a second one for new outlets to be installed.

  13. #13
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    What is your total amp draw expected? Blower will be off most of the time anyway. Likely one 20A circuit will suffice.

  14. #14
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    The tub install instructions say: "The pump and blower are designed for use with an independent 15 amp, 120V electrical power supply protected by an over current protection device rated not more than 15 Amp."

  15. #15
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by ballvalve View Post
    Seen MANY panels in closets. Never saw a fire. .
    I have also seen panels in the bathroom. They used to do this sometimes before the code prohibited it.

    I am sure the NFPA could quote case histories of fires or shock hazards caused by such location. It wasn't a good idea when it was done, and now it is against code.

    Actually, besides the fire/moisture issues, I believe part of the reason for the restriction is that they like the panels to be visible and readily accessible.

Similar Threads

  1. Split 110v off a 230v branch circuit?
    By jeffeverde in forum Electrical Forum discussion & Blog
    Replies: 19
    Last Post: 12-18-2009, 03:23 AM
  2. 220v dryer out conversion to 110v?
    By petergunn in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 10-21-2009, 05:14 AM
  3. Tracing a 110v outlet circuit fault
    By Keith Wolf Ent in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 06-15-2008, 07:18 AM
  4. Should mains be 110v or 120v?
    By dgold in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 07-25-2007, 07:43 AM
  5. 110v or 220v??
    By mycard00 in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 05-25-2006, 07:42 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •