    Default 220v to 110v

    I have a 50amp 220v line (3 wire plus ground) in my master bath that is hard-wired to a hot tub. Remodeling the bathroom and replacing the hot tub with a 110v air bath. Can I use the 220v line to feed a sub-panel (I would hide it in a closet in the bathroom) and then branch two 110v circuits out of the sub-panel?

  2. #2
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Post a link to the specs for your hot tub.

  3. #3
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    It's 18 years old, I can't even find it on the manufacturers website.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by StatManLV View Post
    I have a 50amp 220v line (3 wire plus ground) in my master bath that is hard-wired to a hot tub. Remodeling the bathroom and replacing the hot tub with a 110v air bath. Can I use the 220v line to feed a sub-panel (I would hide it in a closet in the bathroom) and then branch two 110v circuits out of the sub-panel?
    NO

    You can not put a panel in the bathroom or in a closet.

    Yes you can use the branch circuit to feed a panel as long as the conductors are protect at or below the ampacity of the conductors.
    The panel can not face in the bathroom or a closet but can be in the same wall as long as it faces out of these places.

  5. #5
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    Quote Originally Posted by jwelectric View Post
    NO

    You can not put a panel in the bathroom or in a closet.

    Yes you can use the branch circuit to feed a panel as long as the conductors are protect at or below the ampacity of the conductors.
    The panel can not face in the bathroom or a closet but can be in the same wall as long as it faces out of these places.
    Can you explain why it can't be in the bathroom closet?

  6. #6
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    It is an electrical code issue (NEC). Panels are not allowed in closets or bathrooms.

  7. #7
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    Bummer, thanks for the clarification. Guess I need to go to plan B

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by StatManLV View Post
    Can you explain why it can't be in the bathroom closet?
    Well in a closet we have all kinds of stuff like cloth that will burn real easy. In the bathroom we have a lot of moisture in the form of a vapor such as steam and other things like this.

    Besides all this it is a violation of 240.24(D)&(E) of the NEC. (D) says no overcurrent devices in a closet and (E) says no overcurrent in a bathroom. Now if you wanted to set a panel in either location it would be okay just as long as you didn't install any overcurrent devices such as fuses or breakers.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    I think you would need to run another cable. While neutral is connected to ground in the main panel, a subpanel needs the neutral and ground to be separate, along with the two legs (i.e. a 4-wire cable, not three). The neutral is supposed to carry the return current, not the ground wire. The ground is for safety, not current for normal operation. A 240vac device does not need the neutral lead, but a 120vac circuit does.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY Junior Member StatManLV's Avatar
    Join Date
    Nov 2010
    Location
    Cedar Rapids, IA
    Posts
    17

    Default

    Quote Originally Posted by jadnashua View Post
    I think you would need to run another cable. While neutral is connected to ground in the main panel, a subpanel needs the neutral and ground to be separate, along with the two legs (i.e. a 4-wire cable, not three). The neutral is supposed to carry the return current, not the ground wire. The ground is for safety, not current for normal operation. A 240vac device does not need the neutral lead, but a 120vac circuit does.
    The current cable is a 4 wire cable.

  11. #11

    Default

    Quote Originally Posted by jwelectric View Post
    NO

    You can not put a panel in the bathroom or in a closet.
    You can not put a panel in the dwelling bathroom or in a clothes closet.


    Subtle but important difference.

  12. #12
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by 220/221 View Post
    You can not put a panel in the dwelling bathroom or in a clothes closet.


    Subtle but important difference.
    Very true and thank you

Similar Threads

  1. Split 110v off a 230v branch circuit?
    By jeffeverde in forum Electrical Forum discussion & Blog
    Replies: 19
    Last Post: 12-18-2009, 03:23 AM
  2. 220v dryer out conversion to 110v?
    By petergunn in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 10-21-2009, 05:14 AM
  3. Tracing a 110v outlet circuit fault
    By Keith Wolf Ent in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 06-15-2008, 07:18 AM
  4. Should mains be 110v or 120v?
    By dgold in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 07-25-2007, 07:43 AM
  5. 110v or 220v??
    By mycard00 in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 05-25-2006, 07:42 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •