Thread: P-trap Alternatives?

  1. #1
    DIY Junior Member turnerAK's Avatar
    Join Date
    Nov 2010
    Location
    Alaska
    Posts
    5

    Default P-trap Alternatives?

    I am remodeling a basement bathroom. The location for my new shower drain is directly above a main line to the septic. There isn't room for a p-trap right at the shower so my contractor ran the line directly into another pipe about 3 feet away. He says that he couldn't get a trap to fit in the space he had. This concerned me and when I asked him about it he informed me that a local plumber had said that occasionally you have to 'do what you can' when it comes to subgrade drains. The shower is vented and there do not seem to be sewer gases spewing from the drain.

    Are there occasions when it is acceptable to not trap a low-level shower drain?

    Are there alternatives to a formal in-line trap that can be utilized at the drain entrance itself? Maybe a water-gasket device similar to a toilet?

  2. #2
    In the Trades Jerome2877's Avatar
    Join Date
    Aug 2009
    Location
    BC
    Posts
    336

    Default

    No all drains must be trapped, you either need to open the floor and install one or raise the base if there is no room. Also fire the contractor he is jeopardizing your health and anyone else who lives in the house.

  3. #3
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,460

    Default

    I agree Fire the Contractor!

  4. #4
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    6,844

    Default

    Not sure what you mean by a "water-gasket device similar to a toilet". Toilets have a built in P trap. Either you or someone is inventing a term as far as I can tell. Get a real licensed plumber and forget about the contractor. He obviously doesn't shinola about plumbing.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,556

    Default

    quote; I asked him about it he informed me that a local plumber had said that occasionally you have to 'do what you can' when it comes to subgrade drains

    Either he was guoting an "anonymous source", or THAT plumber did not know what he was talking about, or he was intentionally misinterpretting what he was told so his solution would seem correct. We DO "do what you have to do"", BUT that only means you have to figure out HOW to do it correctly, NOT how to avoid the code requirements, and that applies to ALL construction, not just remodeling. If you do not have a "P" trap you do NOT have to have a vent. Do NOT enclose that drain until you have a "real" plumber correct it.
    Last edited by hj; 11-19-2010 at 05:42 AM.

  6. #6
    DIY Junior Member turnerAK's Avatar
    Join Date
    Nov 2010
    Location
    Alaska
    Posts
    5

    Default

    Thank you to everyone for the great advice. I will ensure that the drain gets connected correctly and meets code prior to closing it up.

    I realize now that my "water-gasket device similar to a toilet" was a poor choice of words, thank you Swart for pointing that ambiguity out! After a bit of digging, I found a product that would fit the description of an alternative that I'd like an opinion on. The device is called a 'TrapGuard' made by ProVent Systems. http://www.trapguard.com/ I have contacted their technical department and they claim that their product can be used for floor drains, shower drains, mop sinks etc. and is guarenteed for the life of the drain. When asked about code they said it falls under the 'other viable alternative' clause. Has anyone used this product? What is your opinion of the product?

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    19,228

    Default

    Ideally, you'd move the drain a little so a p-trap would fit. This might entail a lot of juggling things around. But a 2" trap does require some depth (most any place in the US requires a 2" drain line and trap). I'm not sure if it is allowed to put a bend in the riser to the drain from the p-trap, but if so, that might let you jog around the main drain to get enough depth. Or, worst case, you move the main line a bit. Then, the other big thing is at what depth is that main line? The drain water can't try to flow uphill from the p-trap. If the outlet of the p-trap is too low to get into the main drain line by gravity, then you have a whole other problem.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer

  8. #8
    Master Plumber-Gas Fitter shacko's Avatar
    Join Date
    Jan 2006
    Location
    Rosedale, Md
    Posts
    561

    Default

    Quote Originally Posted by turnerAK View Post
    Thank you to everyone for the great advice. I will ensure that the drain gets connected correctly and meets code prior to closing it up.

    I realize now that my "water-gasket device similar to a toilet" was a poor choice of words, thank you Swart for pointing that ambiguity out! After a bit of digging, I found a product that would fit the description of an alternative that I'd like an opinion on. The device is called a 'TrapGuard' made by ProVent Systems. http://www.trapguard.com/ I have contacted their technical department and they claim that their product can be used for floor drains, shower drains, mop sinks etc. and is guarenteed for the life of the drain. When asked about code they said it falls under the 'other viable alternative' clause. Has anyone used this product? What is your opinion of the product?
    That thing you want to use is a device to replace a trap which I'm sure is not approved in most jurisdictions.

  9. #9
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    594
    Blog Entries
    1

    Default

    No it is supposed to be used with a p trap ! Not in place of a trap !

    It is so on drains that do not get used a lot you don't have to install a trap primer to

    keep the water seal in p trap and also if you have a main line blockage you don't have raw

    sewage backing up out of the drain !
    MACPLUMB 777
    E-MAIL JERRYMAC@TROJANWORLDWIDE.COM
    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER AND BOILERS SINCE JAN, 1989
    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT

  10. #10
    DIY Junior Member turnerAK's Avatar
    Join Date
    Nov 2010
    Location
    Alaska
    Posts
    5

    Default

    The representative from TrapGuard claims that it replaces the p-trap entirely. He says the product is air-tight and warrantied. He mentioned that there is nothing wrong with using it on a shower drain despite the drain being used daily for showers. Also their literature claims it can operate under minimal pressure head. In fact, it will drain the slightest of drips all the way up to 33gpm. Any other thoughts?

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,556

    Default

    IT is a flexible "elephant trunk" that curls up and closes. After a period of time the plastic will get hard and either NOT open allow drainage, or close to keep odors out. In other words, it is like an AAV, used when the person does not know how to do it correctly, or does not want to spend the time doing it, without worrying about its long term consequences.

  12. #12
    Homeowner geniescience's Avatar
    Join Date
    Nov 2005
    Location
    humid summers hot, humid winters cold
    Posts
    2,152

    Default

    been seen before. No good. Every time someone raises the subject of this "Trap Guard" it is for a different reason, and that is STRANGE. Methinks a product should know what it is good at. Now someone is asking if it can replace an Entire P Trap. Wow!

  13. #13
    Plumber Winslow's Avatar
    Join Date
    Dec 2005
    Location
    Hawaii
    Posts
    448

    Default

    Quote Originally Posted by turnerAK View Post
    Thank you to everyone for the great advice. I will ensure that the drain gets connected correctly and meets code prior to closing it up.

    I realize now that my "water-gasket device similar to a toilet" was a poor choice of words, thank you Swart for pointing that ambiguity out! After a bit of digging, I found a product that would fit the description of an alternative that I'd like an opinion on. The device is called a 'TrapGuard' made by ProVent Systems. http://www.trapguard.com/ I have contacted their technical department and they claim that their product can be used for floor drains, shower drains, mop sinks etc. and is guarenteed for the life of the drain. When asked about code they said it falls under the 'other viable alternative' clause. Has anyone used this product? What is your opinion of the product?
    I have never heard of an "other viable alternative clause". Seems more like a " if you can't dazzle them with brilliance then baffle them with bullshit" clause.

    Where I work the inspectors tell you if you can't do it legally then you can't do it at all. There is no provision where it is ok to just do what you have to do. In most cases people tell you that because they either don't have the knowledge and experience to give you a viable solution or they don't want to have to pay for the cost of doing it properly.

  14. #14
    Master Plumber-Gas Fitter shacko's Avatar
    Join Date
    Jan 2006
    Location
    Rosedale, Md
    Posts
    561

    Default

    Quote Originally Posted by MACPLUMB 777 View Post
    No it is supposed to be used with a p trap ! Not in place of a trap !

    It is so on drains that do not get used a lot you don't have to install a trap primer to

    keep the water seal in p trap and also if you have a main line blockage you don't have raw

    sewage backing up out of the drain !
    Take a look at the video, they are selling that thing as a trap replacement!

  15. #15
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    594
    Blog Entries
    1

    Default

    The name says it all ! Trap guard "not" trap replacement !

    No where in the video or anywhere else did i see or hear anything that says it will

    replace a p trap ! ! !
    MACPLUMB 777
    E-MAIL JERRYMAC@TROJANWORLDWIDE.COM
    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER AND BOILERS SINCE JAN, 1989
    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT

Similar Threads

  1. Sewer sleeve alternatives
    By ddutchover in forum Plumbing Forum Discussion & Blog
    Replies: 1
    Last Post: 10-30-2010, 07:36 PM
  2. Kinetico alternatives?
    By Mastiff in forum Water Softener Forum, problems, installation and reviews
    Replies: 37
    Last Post: 09-07-2010, 10:47 PM
  3. Outdoor Faucet Alternatives for Summer Use
    By lc1983 in forum Plumbing Forum Discussion & Blog
    Replies: 1
    Last Post: 06-09-2008, 02:28 PM
  4. sump pump alternatives
    By jcress in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 08-01-2006, 08:38 AM
  5. Toto Dartmouth Alternatives and GMax vs. PG
    By deej in forum Toilet Forum discussions
    Replies: 3
    Last Post: 12-14-2005, 05:09 AM