    A review on the kitchen faucet I am interested in stated that "The water lines on this faucet are smaller than my existing faucet, so my water pressure has diminished considerably." The specifications on the faucet list a "Connection size" of 3/8" Compression. If I hadn't read the review I would have purchased the faucet, however, my water presser isn't that hot and I am concerned that the "connection size" could be an issue. Other faucets have a 1/2" connection size. So, can I blindly purchase a faucet based on looks, or do I need to take connection size into consideration?

    TIA

  2. #2
    One who lurks Basement_Lurker's Avatar
    Join Date
    Jun 2007
    Location
    Victoria, BC
    Posts
    668

    Default

    It makes no difference. The outlet on your shutoff valve is 3/8, and the supply tubing you would be using is 3/8. A number of kitchen faucets are now coming with the option of having the 3/8 flex lines already installed directly into the faucet body.
    Broken promises don't upset me. I just think, why did they believe me? -Jack Handy


    www.blackbirdkitchenandbath.com

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The Feds have put limitations on the flow rate of many valves used in a home. You can easily reach that max flow with a 3/8" line. There may be some older ones still on a shelf somewhere, but even then, a 3/8" supply line is/was fairly typical.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    The restriction is at the aerator, not the supply lines.
    We've been using 3/8" for over fifty years.

    Shower heads, kitchen faucets and bathroom faucets all have restricters in place, but not at the supply line.

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Even when the faucet had 1/2" IPS inlet connections, the internal tubing was much smaller. And for years, ALL the flex lines we have used were the same ( approx 3/8) tubing, just with 1/2 or 7/16 or 3/8 ends on it.

  6. #6
    DIY Junior Member sobershea's Avatar
    Join Date
    Sep 2010
    Location
    Michigan
    Posts
    2

    Default

    Thanks for all the input. Faucet is ordered. Thanks again!

  7. #7
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Using this
    http://www.irrigationtutorials.com/copperloss.htm
    and fitting an equation to the values given for type K copper at 2 GPM, for a 3/8" tube the pressure loss will be twice as much as for 1/2", 8 PSI rather than 4 PSI, but this is per hundred feet of pipe.
    Fuhgedit.
    Last edited by Thatguy; 11-16-2010 at 02:08 PM.

Similar Threads

  1. Stupid Newbie Question - Leaks in new faucet connection
    By Timber47 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 08-13-2010, 07:25 AM
  2. Outside faucet has wrong thread size (pipe threads vs hose threads?)
    By NiceMustang in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 23
    Last Post: 01-21-2010, 05:36 PM
  3. size hole for single hole faucet
    By bobbieK in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 04-14-2009, 01:31 PM
  4. Size a faucet to the room size?
    By chrisexv6 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 10-06-2008, 07:09 AM
  5. Connection Leaking on Frost Free Faucet
    By groovychic in forum Irrigation / Sprinkler Forum
    Replies: 3
    Last Post: 08-14-2007, 06:13 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •