    Default Tub/Shower Rough In

    Name:  073a.jpg
Views: 6375
Size:  39.9 KB
    Does anyone see any thing wrong with this tub/shower rough in?

    2" branch, 1 1/2" vent, 2" trap reduced to 1 1/2" to pick up the tub drain.


    Name:  074a.jpg
Views: 5784
Size:  41.6 KB
    In particular can the cleanout be in the 1 1/2" vent line? My (the 2" branch line is 64" thus the clean out) I haven't glued this yet so I can change it if need be.

    Thanks for taking a look.

    Jason

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    The cleanout is supposed to be "full size", i.e., the size of the drain line. HOW are you going to access that cleanout if it is under/behind the tub?

  3. #3
    DIY Junior Member x81sd's Avatar
    Join Date
    Oct 2010
    Location
    San Diego, CA
    Posts
    3

    Default

    I have an access panel that will be installed in the wall behind. Table 7-6 of the California Plumbing Code has the minimum cleanout size for a 2" line as 1 1/2" i'm just trying to figure out if it can be in the vent line in this configuration.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    The reason the "cleanout" can be 1 1/2" is that the plug's o.d. is almost 2", which makes it equivalent to a "full size" cleanout on a 2" line.

  5. #5
    DIY Junior Member x81sd's Avatar
    Join Date
    Oct 2010
    Location
    San Diego, CA
    Posts
    3

    Default

    So if I change the Wye to the Sanitee with the cleanout plug to 2" can I continue after that with a 1 1/2" vent after the cleanout?

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    Absolutely. Just glue a 2 x 1 1/2 bushing in the top of the c.o. tee. And you CAN use a "cleanout tee" which has a tapped opening for a plug, instead of that sanitary tee and adapter. If you do use the tee, they make a "spigot female adapter" which inserts into the opening so you do not have to use a short piece of pipe. Either of these two ways would let you turn the tee facing the access opening rather than sideways like you have it now.
    Last edited by hj; 11-13-2010 at 07:11 AM.

  7. #7
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I'm more concerned about lining up that drain and the lack of an overflow if it is a tub.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    LOOK at the picture. That big "circle" IS the overflow fitting.

Similar Threads

  1. Rough Plumbing for Delta multiple shower heads in Tub/Shower?
    By jsarin1 in forum Shower & bathtub Forum & Blog
    Replies: 6
    Last Post: 10-15-2010, 08:22 AM
  2. rough in tub/shower valve
    By GolfnRL in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 01-13-2009, 07:10 AM
  3. Tub/Shower Rough In Valve
    By A Girl Can Do It in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 06-02-2007, 05:39 PM
  4. Shower rough-in...how do I do this?.
    By drkona in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-18-2007, 05:04 PM
  5. Shower valve rough-in, PEX...
    By mikepdaviskc in forum Shower & bathtub Forum & Blog
    Replies: 5
    Last Post: 02-14-2007, 09:48 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •