    Default Wire gauge for new double-oven?

    Hi all. I asked this question once before, but it was for a single oven. My wife decided she wanted the double, so I need to ask again. Some of the gauge-to-amperage ratings are confusing, so let me ask straight out: for an oven thats 6.9kw @ 240V, with approximately a 40' run from the breaker panel, what gauge wire would you use?

    Its basically this model: GE 30" double oven. We have last years' model, but otherwise, its virtually identical.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    The specifications call for a 30 amp breaker, so you need 10 gauge wire minimum.

  3. #3
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    And with 80' of a #10 AWG copper conductor and a 6900 W/240 V = 29 A draw, if you see more than a 2.3 volt drop in the 240 vac measured at the oven when you turn it on there is a bad connection somewhere.

  4. #4
    DIY Member Artie's Avatar
    Join Date
    Nov 2009
    Location
    Jacksonville, Fl
    Posts
    46

    Default

    Thanks for the fast reply's. #10 it is then.

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    The spec sheet and the install instructions call for 40 amps. I hope the OP gets a second opinion, rather than jump on the first electrical help he got from the PLUMBERS forum!!!!!!!

  6. #6
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    29 A on a 40 A breaker should be enough derating.

  7. #7
    DIY Member Artie's Avatar
    Join Date
    Nov 2009
    Location
    Jacksonville, Fl
    Posts
    46

    Default

    I always check these forums for several days, (sometimes weeks), before I make a move.

    Going with a 40 amp breaker opens a new can of worms. The original oven was an older Lady Kenmore double oven, and it used a dual-30A breaker. I was hoping to reuse that one. This is an old Federal Pacific breaker panel, which doesn't have a very good reputation. If I need to replace that breaker, then I really need to replace the whole panel.

    But if I must, I must.

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by Artie View Post
    I always check these forums for several days, (sometimes weeks), before I make a move.

    Going with a 40 amp breaker opens a new can of worms. The original oven was an older Lady Kenmore double oven, and it used a dual-30A breaker. I was hoping to reuse that one. This is an old Federal Pacific breaker panel, which doesn't have a very good reputation. If I need to replace that breaker, then I really need to replace the whole panel.

    But if I must, I must.
    What you said before was that this was a:
    Quote Originally Posted by Artie View Post
    for an oven thats 6.9kw @ 240V, Its basically this model: GE 30" double oven. We have last years' model, but otherwise, its virtually identical.
    When I go to the site you posted it tells me that for the oven you posted all that is needed is the 30 amp circuit.
    Unless you bypass all the controls on this oven you will never get the full load draw on this oven therefore voltage drop would not be an issue.



    Connect this oven to the same circuit that the old one was connected to and go to bed.
    Last edited by jwelectric; 11-08-2010 at 05:22 AM.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,374

    Default

    It is my understanding that the wire size is determined by maximum draw. But, when inspected, it must ALSO abide by the manufacturer's instructions. So, if they call for a 40A breaker, depending on your inspector, he may require one, too. That would require the appropriately sized wiring to it. Resistance heaters momentarily draw more current when they are energized than their steady state. Their resistance changes as they heat up to limit the operating load. So, for a short period of time, they could exceed the 30A supply (say you turn both ovens on at the same time to preheat them). It probably wouldn't trip the breaker since it happens fairly fast, but it could be an issue. From a safety issue, it probably isn't one, but if it trips, it could ruin your supper! Also, keep in mind that if the voltage drops in a brownout, you draw more amps, and your safety margin gets much smaller.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY Member TWEAK's Avatar
    Join Date
    May 2009
    Location
    Bay Area CA
    Posts
    83

    Default

    I would take this as a great motivation to change the Federal Pacific panel. Those things are scary, and have history. IMO, nothing to trifle with. Plus, most of the breakers you can get for them at this point - since they are long since out of business - are rebuilt. Even the new ones had a reputation for not tripping under overloads. In adition to the busbar issues. Of course if you go that route, you can increase the breaker size if needed.

  11. #11
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by jadnashua View Post
    Resistance heaters momentarily draw more current when they are energized than their steady state.
    For Nichrome it might be 10% higher. Its temperature coefficient of resistance is very small.

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,602

    Default

    The double oven at the link he posted specifies: 240v=6.9 kv; 240v= 30 amps. If he has a different oven then there is no way we can comment on that without the new model number's specifications. Or if he HAS the new oven, then the rating plate will give the proper amperage. I have done almost as much electrical work as plumbing. In fact, I have done trouble shooting FOR electricians.

Similar Threads

  1. Double oven and cooktop wiring - connecting three #6 wires
    By jhodgens in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 11-06-2010, 02:19 PM
  2. Installing a Dryer 30 Amp power cord, 120/240 volt. what gauge wire?
    By 87vertgt in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 09-30-2009, 10:15 AM
  3. wire gauge change mid circuit
    By rockycmt in forum Electrical Forum discussion & Blog
    Replies: 16
    Last Post: 01-09-2009, 11:29 AM
  4. breaker size for 12 gauge wire
    By whoazone in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 10-20-2008, 05:02 PM
  5. heavy gauge bare copper wire
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 03-26-2008, 07:11 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •