240v wall thernostat works, but...

Users who are viewing this thread

Ken Tannenbaum

New Member
Messages
17
Reaction score
0
Points
0
I installed two baseboard heaters running off a 240v bi-pole thermostat and first wired it incorrectly blowing the circuit. The short happened at one of the radiators, not the thermostat. Now it's wired right and works, except that the instructions with the thermostat say it should make a clicking sound when it goes on, which it doesn't do. Is there a chance I damaged the thermostat? And could that be dangerous? Thanks!
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Does it work properly? IF so, then you did not damage it, regardless of whether you hear the contacts click or not. If the contacts did NOT open, or close, which creates the "click" the heaters would either not turn on or not turn off.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
Switches are supposed to have a "snap action" so the arc during switching doesn't last too long. They use little magnets and springs to do this.
I guess it's possible that this t'stat doesn't have this snap action anymore and so it won't last long. Can't say for sure, though.

One way to check this would be to put an AM radio nearby tuned between stations. Arcs radiate radio waves and a drawn out arc should sound like a crashing sound for a half second or so, rather than just a 'pop' sound.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
The switch has two poles, but breaking either one will cause the heater to stop working. One of them could be welded closed, and that could prevent the two from snapping back...it would depend on the construction of the switch. Or, it could be working fine. You could find out if that is the case with a meter. With the power off, the connection between one side of the switch and the other should be open on both poles. Or, with the power on, measure from the output of one side to the input of the other (do it both ways). If it is zero, the pole is open, if it reads 240vac, that pole is welded shut.
 

Thatguy

Homeowner
Messages
1,454
Reaction score
3
Points
0
Location
MD
With the contacts closed confirm that you have less than 30 millivolts across those closed contacts with rated current flowing through them.
More than 100 mV is bad.

Open contacts should have 240 v across them.
 