    Default Well done, water hammer

    Hi all,

    New pump is about 10 times faster at filling than the old one and now I have some serious hammer at pump on and off.

    I did a search here but did not find anything related to pump turn/off one. I am blaming my Search terms more than the Search system.

    I have a WellMate WM-25 pressure tank with the air pressure set at 28-psi for 30-50. If I turn off the power to the pump and let the tank empty, I hear the pressure switch click at 30 and right about 28, the flow from the tank drain bib cuts out. Not sure if that is important but thought it might save a question from the experts.

    What are my options?

    Thanks

    Harry

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,150

    Default

    If the piping is not properly supported in the building it can cause a banging noise. Water hammer in a well system is commonly caused by a faulty check valve or a check valve installed in the wrong place.

  3. #3
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Try turning up the shut off pressure to about 75 or 80 and report if the the OFF hammer stops. And or try 40 to 75 as your switch setting. Fast moving water does not like to be stopped quickly. You will have a harder time with the ON noise, which if not some weird check valve issue, is simply loose pipes absorbing a hydraulic shock.

    Maybe you have too much pump for your system....

  4. #4
    Mechanical Engineer WellHead's Avatar
    Join Date
    Oct 2010
    Location
    Arizona
    Posts
    34

    Default

    Thanks for the replies. I will check the pipes for loose attachments and saddles.

    To much pump? The one taken out was a 19-gpm and this is a 10, so I am thinking probably not, but I am not knowledgeable in this area.

    I'd rather not try the 75-psi thing as the copper and PVC plumbing in this place was installed in 1978. The DIY owner/builder had limited plumbing skills and it is a mess of pipes. Probably 50% of the joints and valves have leaks that have calcified and sealed. I fear bumping the pressure may present we with a wonderland of small fountains.

    One of these days I will re-do it all.

    Harry

  5. #5
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Water hammer can [will] produce shock pressures of 150 to 500 psi and more. Pipes are certain to leak with that impact, but they are designed to live forever with consistent pressures under their rating.

    "hammer" if that is what it is, will open those leaks and provide a shower stall long before a 25 or 30 PSI increase in constant pressure.

    Most PVC and copper can easily see 120 psi forever, and not be compromised. I believe 1" PVC is rated for 450PSI. And thats max working pressure. Those little rubber hoses on excavators run happily for years on 4500 PSI.

    You might consider a dole valve to reduce flow a bit, or a CSV. If you have a valve between the pump and the tank, throttle back the flow as a test. Be sure you have a pressure relief valve inside that circuit.

    10 times faster fill rate on a 19 vs 10 gpm pump tells me something is wrong with your calcs, or you have far too much Horsepower under the pump head.

  6. #6
    Mechanical Engineer WellHead's Avatar
    Join Date
    Oct 2010
    Location
    Arizona
    Posts
    34

    Default

    ..10 times faster fill rate on a 19 vs 10 gpm pump tells me something is wrong with your calcs,

    Nope, the 19-gpm is 20 years old -- plus -- there was a small hole about 3' above it. As the hole got bigger the flow reduced and then finally the pressure started dropping as the hole got even bigger.

    Harry

  7. #7
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Okay, forgot your hole. What is the flow rate at your shut off pressure setting according to the pump chart? How many HP? Pumping depth? If you have a real impact and noise at shut off, you should try some of the ideas above.

  8. #8
    Mechanical Engineer WellHead's Avatar
    Join Date
    Oct 2010
    Location
    Arizona
    Posts
    34

    Default

    Quote Originally Posted by ballvalve View Post
    What is the flow rate at your shut off pressure setting according to the pump chart? How many HP? Pumping depth? If you have a real impact and noise at shut off, you should try some of the ideas above.
    For the depth etc, the 10GS15 is right on it's sweet spot of 9.4gpm at 50-psi shut-off.

    I am going to try a Sioux Chief hammer arrestor at the top of the lift pipe. It has a Tee sitting vertically with a plug in it. I will replace the plug with an elbow and then the arrestor. I can't sit the arrestor straight up because of the lid on the well head housing. But Pascal pretty much assures me the elbow will be OK.

    Harry

  9. #9
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    One of the best hammer arrestors Sioux does not want you to know about is a soft 100' garden hose left on with a shut off valve on the end.

    Cheaper and even more useful than a 30 dollar stick of copper. .... Even better if you drain it now and then, close the hose end valve and re-open the hose bib.

    Saw a hammer arrestor - 4" pipe riser full of rubber balls. worked great.

    One last arrestor is a adjustable pressure relief valve for 7$ set to drip at 50PSI and then add 1/4 turn to the spring. No more 400PSI surges, just a little leak for a moment.

  10. #10
    Mechanical Engineer WellHead's Avatar
    Join Date
    Oct 2010
    Location
    Arizona
    Posts
    34

    Default

    Quote Originally Posted by ballvalve View Post
    One of the best hammer arrestors Sioux does not want you to know about is a soft 100' garden hose left on with a shut off valve on the end.
    Interesting, but I am guessing (from your avatar) you live in CA. That hammer arrestor would only work 6 months of the year here.

    The hammer is not going beyond the two filters and so they are obviously taking care of part of it.

    Interesting thought on the pressure relief though. To be fair, the Sioux arrestor is only $12 and no leaks.

    Harry

  11. #11
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    It freezes here nicely, but for only a week at a time, then its sping again for a few weeks. I leave the hose cracked and build a nice ice sculpture with it. Thats my windshield defroster hose.

    I would call Sioux and ask about the flow rate of 10gpm - remember these are for fixtures, and I know I don't get 10 gpm out of my sink or washer. Certainly don't try their "mini's"

    Those clear plastic filters will not tolerate any hammer for long. And the PRV could be hosed off to a drain.

    What you really want is a valve that SLOWS the flow to 1 or 3 gpm just before shutoff, but outside of a CSV - whole different story - I cannot think of one.....

  12. #12
    Mechanical Engineer WellHead's Avatar
    Join Date
    Oct 2010
    Location
    Arizona
    Posts
    34

    Default

    Quote Originally Posted by ballvalve View Post
    I would call Sioux and ask about the flow rate of 10gpm - remember these are for fixtures, and I know I don't get 10 gpm out of my sink or washer. Certainly don't try their "mini's"
    Ha! Good thought Dude, **but** I seem to be being ignored by Sioux head-office. I also asked two of their dealers and got the old, "we just sell them, we don't know s..t about them" reply. Guess which two dealers will not see my credit card number?

    The PRV could dribble on the garage floor. Our humidity rarely gets about 30% so it would evaporate before hitting the floor.

    It looks like a PRV or CSV then. I will check with the well guy who put the pump down there. When I told him about the hammer, he didn't seem very interested or concerned. It's a third generation drilling company so I am sure he must have heard of the issue.

    Harry

Similar Threads

  1. Water Hammer?
    By Sixdays in forum Pumps and Tanks Well Forum & Blog
    Replies: 29
    Last Post: 06-07-2010, 04:32 AM
  2. Water Hammer?
    By bdzerneke in forum Water Softener Forum, problems, installation and reviews
    Replies: 29
    Last Post: 02-14-2010, 06:31 AM
  3. is this water hammer?
    By ptero in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 08-31-2009, 02:01 PM
  4. Demo Hammer/Roto Hammer--Help me choose
    By rshackleford in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 17
    Last Post: 07-03-2007, 05:34 PM
  5. Water Hammer when Clothes Washer shuts off water
    By adenwork2 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-22-2006, 04:45 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •