    An Intellicon won't buy you any condensing efficiency the way a Munchkin Contender would, but a 6x oversized mod-con would be a bit silly, and would likely need a buffer tank to keep from short cycling (unless you're a hydronic-design genius and can set up the place perfectly as a single zone.) A right-sized Contender is around two grand new, with warranty, etc.

    Installing & setting up a mod con is more than a simple plumbing project, and not a suitable DIY project. (Just buying the necessary tools & training to do it right would be expensive.) If you're undaunted by that, I STRONGLY advise you to seek out free/cheap training sessions sometimes offered by mod-con manufacturers (usually through distributors), but they may require you to have a plumbing license w/ gasfitter certification to even attend. There are many issues that come up, eg, modulating burners are much more sensitive to gas pressure transients etc than old-school stuff, just for starters. If you have an 83% AFUE cast iron beast already in service that isn't on it's last legs, setting it up to run at best efficiency for the load at hand with an Intellicon is clearly the best financial decision. If gas prices quadruple you can revisit the mod-con idea, but the costs will be more than just the boiler price tag- there are many system design factors that need to be done in advance to get the most out of it.

    Measure the burn lengths of the existing setup. If you re-configure to run it as a 2-zone system the burn lengths would remain the same, but the duty cycle would go up, increasing the as-installed AFUE (lower idle time==lower standby loss). Unless you've done the manual-J and measured the radiation size to verify the balance, odds are the two systems are NOT inherently balanced well enough to run it as a single zone. But with an economizer you'd cut the number of cycles roughly in half (about the same as running it as a single zone) lengthening the burns, yet shaving 10-15% off the overall burner on-time over the course of a day for a 10-15% fuel savings. (In grotesquely oversized systems the savings would be more.) Setting it up as a simple 2-zone system with an economizer boiler control IS a reasonable DIY project for somebody with good plumbing skills, and modest electrician skills, and wouldn't require much in the way of re-tuning the radiation size or re-plumbing the near-boiler stuff to guarantee you don't end up with condensing conditions in a non-condensing-tolerant boiler. (You'll get to experience the joys of purging the air out of the system once you have it buttoned back up too! :-) )

    If the system(s) have a boiler bypass or other low return temp protection stratetegy, measure the temp of the return water under a variety of conditions. If it's under 130F for extended periods of time you may have to adjust it. (Often a boiler bypass with a thermostatic mixing valve will work well enough on a boiler that size, but for many a much cheaper ball-valve would be "good enough" if the cold start wasn't too cold for too long.) With your house tightening efforts the average and peak temps of your radiators has been dropping, which may be lowering the average temp of the return water to a relevant temp. For continuous operation 130F would be a hard lower-limit for a cast iron boiler. But running at the lowest allowable return water temp maxes out it's combustion efficiency. For every 10F drop in return water temp you yield about a 2-3 percent reduction in fuel use (a fact incorporated into economizer controls that allow you to program a min boiler temp to be met during calls for heat.) The radiation was probably designed to deliver sufficient heat in the house's pre-insulated pre-air-sealed state at 160F-180F water, but would now likely be able to deliver even design-day heat with 120-140F water.

  2. #17
    DIY Junior Member abernat's Avatar
    Join Date
    Sep 2009
    Location
    Wisconsin
    Posts
    23

    Default

    I am officially daunted. As a "technical" type, I often really underestimate how difficult projects are.

    The current system is set up as two zones (upstairs/downstairs), since that was the easiest way of connecting the pipes. I'll abandon the second boiler and look into purchasing an economizer.

    Moving forward. I can see where to adjust the temperature setting on the aquastat, and it definitely was at 180*. I've turned that down to 150 for now. You're suggesting I continue to turn it down as long as the return doesn't fall under 130? Would I be better off padding the return temperature? There is definitely no bypass of any sort in the system - it's boiler -> zone valves -> radiators plumbed in parallel -> boiler.

    Thanks again for everyone's help!

  3. #18
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,715

    Default

    Quote Originally Posted by abernat View Post
    I am officially daunted. As a "technical" type, I often really underestimate how difficult projects are.

    The current system is set up as two zones (upstairs/downstairs), since that was the easiest way of connecting the pipes. I'll abandon the second boiler and look into purchasing an economizer.

    Moving forward. I can see where to adjust the temperature setting on the aquastat, and it definitely was at 180*. I've turned that down to 150 for now. You're suggesting I continue to turn it down as long as the return doesn't fall under 130? Would I be better off padding the return temperature? There is definitely no bypass of any sort in the system - it's boiler -> zone valves -> radiators plumbed in parallel -> boiler.

    Thanks again for everyone's help!
    The 180F aquastat is the high limit, not the low. Assuming a typical 20-30F delta-T on radiation, keeping it at 160F or above is probably a better bet. Some boiler controls are set up to enable/disable the circulation pumps at the low limit of the boiler, with a certain amount of hysteresis built in, others are just full-flow all the time on the circulation, turning the burner on at the low limit. You might want to figure out the whole shebang now, looking up the specs for the boiler and it's component aquastat(s). When inserting an economizer into the system you typically set the boilers high-limit aquastat to max to keep it from cutting out instead of letting the economizer run that control. See: http://www.designheating.com/pdf/INT...ons%5B1%5D.pdf

    A boiler-bypass pipe is one standard method of keeping the input temp up on systems (particularly high-mass systems where the slug of room-temp return water on a cold starts is large enough to stress the boiler.) It's basically a pipe diverting the boiler output directly to the input, in parallel with the radiation, sized (or valved) such that it mixes enough output water in with return water to keep it above temp:



    A thermostatic mixing valve is used as the adjusting valve would be placed with it's output on the boiler return, hot input on the bypass loop. Dialing it to 130F, when the return temps are lower than that it'll mix in output water to raise it up, then as the radiators heats up it sips less output. If a (much cheaper) ball valve is used it needs to be tweaked in by hand during a system cold-start to figure out how much boiler output mix is necessary for protection, and it'll continue to mix that volume independently of the system temp. No heat is lost from the system though- the boiler just hit's it's steady state temp a little quicker. Insulate all of those pipes to lower standby and distribution losses though- there's no point in putting more heat in the basement than necessary for comfort/freeze control. (Higher basement temp==higher heat loss out the foundation- heat better applied to fully conditioned space.)

  4. #19
    DIY Junior Member abernat's Avatar
    Join Date
    Sep 2009
    Location
    Wisconsin
    Posts
    23

    Default

    I see, thanks. Would it make sense to put in the bypass no matter what to ensure that I'm not going to shock the boiler? I'm definitely capable of working in a loop of that sort and taping a thermometer to the cold return.

    I really appreciate the help!

  5. #20
    DIY Junior Member david_griffin's Avatar
    Join Date
    Feb 2011
    Location
    Denver, CO
    Posts
    25

    Default

    Quote Originally Posted by abernat View Post
    We are not planning to re-split the house, no. It started as a 2-flat and we're recombining it into a single family home.
    .
    If I were you I would install a single heating unit. There are plenty of very efficient German made boilers for example Buderus.

Similar Threads

  1. Opinions wanted on Delta 532, 540, 580
    By bigbird in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 01-31-2008, 03:26 PM
  2. I wanted to introduce myself
    By popawheelie in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 12-13-2007, 05:50 PM
  3. more zones wanted, no more wires
    By msgale in forum Irrigation / Sprinkler Forum
    Replies: 8
    Last Post: 10-11-2006, 05:16 PM
  4. More critique wanted
    By thezster in forum Remodel Forum & Blog
    Replies: 2
    Last Post: 07-18-2005, 02:36 PM
  5. Wanted - Odd Faucet...
    By Phatbrain in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 01-17-2005, 10:50 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •