Thread: Circulating pumps always on

  1. #1
    DIY Junior Member gordonp1's Avatar
    Join Date
    Oct 2010
    Location
    Pittsburgh
    Posts
    2

    Default Circulating pumps always on

    I just got a new boiler installed (Laars Mini-Therm II 160) with two circulating pumps. The plumber wired the pumps to be always on. My old system would turn on the pump only when heat was demanded. The plumber claims that because I have an old system with dirty water and particles, the pumps would be damaged if they are off for a long time. I have two B&G NRF-22 pumps that use together 194 watts - that translates into about $240/year just to run these pumps. It just does not make sense to me. Is he right? I would like to tell him to rewire it so that the pumps start when thermostat turns on.

  2. #2

    Default

    I believe your contractor is right. Replacing pump every few months will be even more expensive, just consider the cost of pump itself, which is $70-250. For example, Taco pumps http://www.pexuniverse.com/store/manufacturers/taco or Grundfos http://www.pexuniverse.com/store/manufacturers/grundfos .

    Do you have any filters or strainers installed in your system?

  3. #3
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by gordonp1 View Post
    dirty water and particles
    Speaking of financial tradeoffs, how much to clean and maintain cleanliness?

    Are those pumps rated for continuous duty?
    Last edited by Thatguy; 10-16-2010 at 10:41 AM.

  4. #4
    DIY Junior Member gordonp1's Avatar
    Join Date
    Oct 2010
    Location
    Pittsburgh
    Posts
    2

    Default

    They are rated for continous duty. I do not have any filter or strainers installed. The old boiler pump ran without any problems for 17 years with a boiler that was about 40 years old.
    We have been in this house for 17 years and no problem with the pump being off when there is no heat demand. I don't mind if the new pumps are on during the heating season but to keep them running from March to October?
    Where can I find information about installing a filter or strainer?

  5. #5
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Apparently seasonal startups are a problem, which they try to overcome with high starting torque, but they don't say the cause of this problem.
    http://www.bellgossett.com/productpa...rts-nrf-22.asp
    Maybe all pumps with clean or dirty water have this problem. Something must seize up.

    I guess another fix would be to periodically run the pump with some kind of timer, say 1 minute on once per day or per week, regardless of water demand.

    One or both pumps failing would cost how much? More than $240 each year?
    Last edited by Thatguy; 10-16-2010 at 07:18 PM.

  6. #6
    DIY Junior Member david_griffin's Avatar
    Join Date
    Feb 2011
    Location
    Denver, CO
    Posts
    25

    Default

    Quote Originally Posted by gordonp1 View Post
    I just got a new boiler installed (Laars Mini-Therm II 160) with two circulating pumps. The plumber wired the pumps to be always on. My old system would turn on the pump only when heat was demanded. The plumber claims that because I have an old system with dirty water and particles, the pumps would be damaged if they are off for a long time. I have two B&G NRF-22 pumps that use together 194 watts - that translates into about $240/year just to run these pumps. It just does not make sense to me. Is he right? I would like to tell him to rewire it so that the pumps start when thermostat turns on.
    He was not right. Pump must run only over certain temperature because if the water is cooler then this water steals heat. Your pumps not only heating your house but mostly cooling rooms. Pumps should stop if no heat demand from the furnace.

Similar Threads

  1. no hot water circulating to upper loop
    By rmeyer in forum Boiler Forum
    Replies: 2
    Last Post: 04-08-2010, 03:47 PM
  2. Hot Water Circulating Pump
    By SAnsari in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 01-13-2009, 07:03 AM
  3. water circulating pump/motor
    By steveleewonder in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 10-13-2008, 06:41 PM
  4. TACO 007 circulating pumps propeller/shaft separation?
    By pkrsiak in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 12-15-2005, 05:21 PM
  5. Leaks in hot water circulating system
    By Jim Curtis in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 09-15-2005, 11:56 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •