Thread: Top Element Electrical

  1. #1
    DIY Junior Member BillM's Avatar
    Join Date
    May 2007
    Location
    Michigan
    Posts
    20

    Default Top Element Electrical

    Good morning All.....
    I'm attempting (1st time novice) to replace Lower element on a GE water heater......shower goes cold after about 15 minutes......from what I've read, and testing of lower element with multi-meter, its shot......so I'm currently draining water heater, and ready to install lower element.....

    I thought I'd replace upper as well, since I'm 1/2 way thru this project as I write this......just got back from HD with an upper element......when I went to disconnect red power, I got some 'minor' sparking......scared me enough to back off of it, but I'm no electrician or plumber? Lower element disconnected without any sparking........a bit nervous, to say the least.....breaker at circuit panel has been shut off, and elements reading 0 volts on the meter.....

    Am I ok to pull out upper element, just to do preventative maintenance, or am I in over my head right now? Whats with the minor sparking?

    Thanks in advance!

    -Bill

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,208
    Blog Entries
    1

    Default

    Are you sure you have the right breaker off?

  3. #3
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    What does your meter say the voltage is on the 2 upper screws on the upper thermostat where the power is connected at?

  4. #4
    DIY Junior Member BillM's Avatar
    Join Date
    May 2007
    Location
    Michigan
    Posts
    20

    Default

    Yes....breaker is "off"......all water now drained from the water heater......I'm thinking I'm just going for the lower element, and go with the theory of "if it isn't broken, don't try to fix it".......so, I'll stay away from top element......

  5. #5
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by BillM View Post
    Lower element disconnected without any sparking
    . . . probably because it has failed to an open circuit, like your multimeter said. Open circuit = no current = no sparks.

    The sparking top element is probably still good, but you can check it more precisely with your meter using the resistance function. Ohms = voltage squared divided by power.
    For 240 V and 4500 W you should get 12 to 13 ohms.

    For safety you need the elements to read zero voltage from pin to pin, and zero voltage from either pin to ground.
    It's the voltage with respect to ground that mostly hurts people. The current then goes through their chests rather than just through their fingers.
    Last edited by Thatguy; 10-10-2010 at 05:43 PM.

  6. #6
    Plumber Winslow's Avatar
    Join Date
    Dec 2005
    Location
    Hawaii
    Posts
    450

    Default

    is this an older house? Are you sure the heater is wired correctly? I got jolted once because even though the breaker was off there was electricity to the heater because of the way it was wired. Hot wire directly to the heater then the loop was broken through the breaker after the heater. Had that happen on a couple of disposers too. Electricity is nothing to fool with.
    Last edited by Winslow; 10-10-2010 at 03:53 PM.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    IF the upper element has power to it, and I cannot imagine how it would spark if it did not, and you have drained the water from the tank, then the element is already shot and has to be replaced. You NEVER work on an electric heater until you are ABSOLUTELY sure that there is no power to it, in any form. The lower element would NOT spark if the upper one was energized, which is the case since the upper one sparked, but that does NOT mean you would not get a shock if you touched the wire while you were grounded.

Similar Threads

  1. Two elements vs. one element
    By comfun1 in forum Water Heater Forum, Tanks
    Replies: 10
    Last Post: 03-03-2010, 11:19 PM
  2. Thermostats : Dual Element in a Single Element Water Heater
    By Synicasm in forum Water Heater Forum, Tanks
    Replies: 4
    Last Post: 11-09-2009, 01:35 PM
  3. Single element thermostat on dual element heater
    By garycase in forum Water Heater Forum, Tanks
    Replies: 9
    Last Post: 07-31-2009, 04:51 PM
  4. I want an indicater light for my element...
    By Pewterpower in forum Water Heater Forum, Tanks
    Replies: 2
    Last Post: 04-02-2009, 07:07 PM
  5. Electrical Engineer allowed to do Electrical work?
    By willijimon in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 03-05-2009, 05:08 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •