    I came across this the other day on a jobsite and had to do a little research. A guy had a Solar heat exchanger installed by a professional company that specializes in this type of system. The problem was the single wall heat exchanger. The company used Propylene Glycol saying it was non-toxic but the msds gave it a "1" for health. The UPC prohibits toxic substances in heat exchangers unless it is double walled. So I had do some research and found out that the Propylene Glycol cannot be used in a single wall exchanger because it IS toxic. The company said that they've never been called on it before and the package says "non-toxic" so what's the big deal. The UPC references some old archaic toxicology book that we had to find to confirm the code call. What a pain in the arse! So the company is now going to use a Glycerin based antifreeze and since Glycerin is ok by code we have to allow it. I can't seem to find what the other ingredients are, probably proprietary information, but still, I don't know if I'd want something that's going to make me just a "little" sick even close to my potable water. Now I'm wondering how many of those systems have been installed with Propylene Glycol? Any thoughts on this one?
    (shoulder shrug)

  2. #2
    DIY Junior Member frankflynn's Avatar
    Join Date
    Oct 2010
    Location
    Palo Alto, CA.
    Posts
    8

    Default

    So was this a closed loop? I'm thinking that if there was a leak in the heat exchanger the domestic hot water is under pressure and would fill then over fill the Glycerin / Glycol side then flood the basement or spew from the roof. At any rate it would be notices and the problem would not be Glycol getting into the domestic water but domestic water getting out.

  3. #3
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    Quote Originally Posted by frankflynn View Post
    So was this a closed loop? I'm thinking that if there was a leak in the heat exchanger the domestic hot water is under pressure and would fill then over fill the Glycerin / Glycol side then flood the basement or spew from the roof. At any rate it would be notices and the problem would not be Glycol getting into the domestic water but domestic water getting out.
    You're presuming that the potable water pressure will always be higher than the glcol loop. Experience indicates otherwise, independently of the installer- pre-charged pressure or PRV settings on the glycol loop.

  4. #4

    Default

    Quote Originally Posted by Inspektor Ludwig View Post
    I came across this the other day on a jobsite and had to do a little research. A guy had a Solar heat exchanger installed by a professional company that specializes in this type of system. The problem was the single wall heat exchanger. The company used Propylene Glycol saying it was non-toxic but the msds gave it a "1" for health. The UPC prohibits toxic substances in heat exchangers unless it is double walled. So I had do some research and found out that the Propylene Glycol cannot be used in a single wall exchanger because it IS toxic. The company said that they've never been called on it before and the package says "non-toxic" so what's the big deal. Now I'm wondering how many of those systems have been installed with Propylene Glycol? Any thoughts on this one?
    (shoulder shrug)
    Generally, you don't need double wall heat exchanger unless you have potable water on one of the sides in your system. For example, in radiant heating systems for snow melt is widely used 30%-40% propylene glycol mix. Does it means you need a double wall heat exchanger? ...

    How old was that solar system?

    --------------------------------------------------------------------
    Will getting a new heat exchanger solve the problem?
    www.brazetek.com/products
    www.flatplate.com

  5. #5
    DIY Junior Member mkiernan's Avatar
    Join Date
    Sep 2011
    Location
    Oklahoma
    Posts
    4

    Default

    You can use propylene glycol in single walled heat exchangers so long as the unit is marked with class 1 substance as recommended by the fda and ipc and the unit is UL listed. the fda website goes into a little more detail but it will meet code.

Similar Threads

  1. Use a Thermostatic Mixing Valve in a Solar Hot Water heat dissipator
    By Herman Hartzler in forum Solar and Geothermal Water Heating Forum
    Replies: 5
    Last Post: 07-28-2010, 08:07 PM
  2. ASME approved heat exchangers
    By patsfan78 in forum Boiler Forum
    Replies: 2
    Last Post: 01-29-2010, 08:48 AM
  3. #10/3 for single wall oven?
    By Artie in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 01-05-2010, 04:47 PM
  4. Heat vent on the shower Wall
    By yomero in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 09-28-2009, 05:57 PM
  5. solar heat for inground pool
    By little buddy in forum Solar and Geothermal Water Heating Forum
    Replies: 3
    Last Post: 02-26-2009, 03:40 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •