    I want to run this water heater, (10 gal., 120VAC, 1650W), at a remote location. (Approximately 20ft. from the breaker box.) Would 12-2 be sufficient?

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    1650 watts is about 13 amps. 12 guage wire is fine.

  3. #3
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    If you have an ohmmeter, before you install this heater check that the element resistance is at approx. (120v^2)/1650w = 8.7 ohms.
    It can't hurt to make sure.

    Their kwh rating for a year is based on it being on 17% of the time. I guess this is some consumer average usage.

  4. #4
    DIY Member Artie's Avatar
    Join Date
    Nov 2009
    Location
    Jacksonville, Fl
    Posts
    46

    Default

    Thanks guys.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    The KW for a heater is the "actual" wattage, not a "kw per year" statistic. The "kw/yr" number creates the "annual cost of operating the heater" which is a completely different thing.

  6. #6
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Speaking of power usage,
    since the element runs on 120v, wiring an electromechanical analog clock across the element for 24 hours or so will tell the heat loss through his R8 insulation.
    If the clock advances 5 minutes every 600 minutes with no hot water being used then his loss is 1650w(5m/600m) = 14 w = 48 BTU/hr.

    I definitely have to find a day job. . .

Similar Threads

  1. breaker size for 12 gauge wire
    By whoazone in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 10-20-2008, 05:02 PM
  2. Wire size question
    By jparrie in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 10-20-2008, 04:46 PM
  3. Intermixing wire size
    By Mr_Magoo in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 08-13-2008, 03:17 PM
  4. 240V electric water heater on 120v circuit
    By miscmail1560 in forum Electrical Forum discussion & Blog
    Replies: 26
    Last Post: 12-12-2007, 04:52 PM
  5. 1 pole, 2 wire or 2 pole 3 wire switch for water heater?
    By bigtime in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 11-04-2007, 05:13 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •