Thread: Can 2 lights (same circuit), 2 switched, be converted into one switch?

Hybrid View

  1. #1
    DIY Junior Member casualfc's Avatar
    Join Date
    Mar 2006
    Location
    New York
    Posts
    12

    Default Can 2 lights (same circuit), 2 switched, be converted into one switch?

    I have a 3 switch plate on my wall. One switch is for an indoor light switch ( 3 wire, as there are 2 on the same line). The other 2 switches are two separate outdoor light fixtures. I would like to install an in-wall timer that controls both outdoor light sets at the same time. Is this possible?

  2. #2
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    Yes, there would be no problem doing that, if, as you say, the lights are powered by the same circuit. Be aware that many
    electronic timer switches require the presence of the circuit neutral wire in the switch box.

  3. #3
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by casualfc View Post
    I have a 3 switch plate on my wall. One switch is for an indoor light switch ( 3 wire, as there are 2 on the same line). The other 2 switches are two separate outdoor light fixtures. I would like to install an in-wall timer that controls both outdoor light sets at the same time. Is this possible?
    I don't quite understand your current arrangement but I can tell you that the timer needs to go in series with the source for all the lights, and between the source and only these light circuits.
    This can get pretty tricky.

    Once you have a wiring diagram (not the same as a schematic) for your existing setup the necessary changes will be obvious.
    Getting this diagram will be difficult, even if your wires follow the color code.
    Make drawings of your existing setups in each box so that you can return to the original configuration if necessary, because the worst outcome is that you end up with nothing working and breakers that trip instantly.

    You'll need clip leads, a DVM, an extension cord, and a test load, e.g., an incand. bulb. A helper will make things go faster.
    I recommend getting one set of lights working at a time. Since switches are cheaper than timers, I'd substitute a switch for the timer until you're sure everything works as planned.
    Last edited by Thatguy; 10-03-2010 at 07:24 AM.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    If you are describing what you have, and what you want to do, correctly, then all you need is the timer switch to replace either of the two switches, and then connect both lights to its "load" side, (if it directional and has one), and abandon the other switch and its "hot wire". Few timers require a neutral for the circuitry, since they use "backfeed" through the light for the neutral.

  5. #5
    DIY Junior Member casualfc's Avatar
    Join Date
    Mar 2006
    Location
    New York
    Posts
    12

    Default

    Thanks for the responses. Here's my plan in my layman's terms. In the wall are 2 switches, each attached to 2 black wires and a ground. The timer does not require a neutral, although it has a red wire for use in 3 way setups. My plan is to attach one black wire from each switch to one black wire each on the timer.
    This leaves 2 questions. 1) For the unused red wire from the timer, can I just cut the wire, or cap it with a wirenut, or both? 2) For the 2 ground wires, can I just connect them and cap with a wire nut, or do I- connect the 2 ground and run a pigtail to the grounding screw on the timer, or connect the 2 grounds, and use a green wire connector with the hook from one ground going to the screw on the timer?
    As you can easily see, this is new to me. Thanks for your help in advance.

  6. #6
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by casualfc View Post
    My plan is to attach one black wire from each switch to one black wire each on the timer.
    Post a link to your timer.

    If your timer controls an internal DPST electromechanical relay then it should be easy. Otherwise you should confirm where each black wire from each wall box goes: to a 120 V source, to a neutral, through a load to a 120 V source or to a neutral, or to somewhere else. Measure with respect to a known good ground or neutral or hot lead while using an incand. lamp across your voltmeter leads.
    Also check if there is 240 V between any two black wires, without using the the lamp.

    If you hook it up anyway without knowing, because of the permutations and combinations possible with hooking up four wires, the odds are overwhelming that it will not work and/or you will clobber the timer.

    At least wear eye protection.
    Last edited by Thatguy; 10-11-2010 at 02:00 PM.

  7. #7
    DIY Junior Member casualfc's Avatar
    Join Date
    Mar 2006
    Location
    New York
    Posts
    12

    Default

    It's this model timer.
    http://www.intermatic.com/products/t...ers/st01c.aspx

    I've also attached the installation portion of the instructions.
    Attached Images Attached Images  

Similar Threads

  1. how many lights in a circuit as per code
    By pedrito in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 10-03-2010, 07:39 AM
  2. Residential Lights and Outlets on Same Circuit?
    By TomBrooklyn in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 08-24-2010, 08:08 AM
  3. lights on GFI protected circuit
    By pmayer in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 11-02-2009, 08:40 AM
  4. Number of lights allowed on a circuit
    By nashkato in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 05-01-2009, 07:37 AM
  5. AFCI Circuit trips when I turn on lights
    By Keith Wolf Ent in forum Electrical Forum discussion & Blog
    Replies: 19
    Last Post: 06-23-2008, 08:15 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •