It would really make no sense to have a limitation on the number of luminaires on a circuit, in the absence of
any information on the power consumed per fixture. I have never encountered such a code limitation, and doubt
that any such exists.
|
|
|
It is my intention to place 24 pot lights around
the perimeter of the house.
24 lights of 50 watts, having of total of 1200
watts.
1200 watts divided by 120 volts gives me 10 amps.
I have placed a new breaker of 15 amps. Wich lead
me to think that I will be OK.
The question that I have is: How many lights I am
allowed asper code in one circuit.
IT is 12 lights ONLY????
PLEASE REPLY..thanks
It would really make no sense to have a limitation on the number of luminaires on a circuit, in the absence of
any information on the power consumed per fixture. I have never encountered such a code limitation, and doubt
that any such exists.
To calculate your total fixture wattage, you need to go by the mfg's max bulb wattage for that fixture. (i.e. I you are using 50watt bulbs but the fixture is rated for using 75 watt bulbs you need to use the 75watt figure to calculate with.) That said, I always try to stay within 80% or less of the circuit rating.(appox 1440 watts for a 15amp circuit)
TreyH
** Not a professional - only a DIYr **
As I have read on other forums about the CEC, 12 is the max.
You need to ask someone in the code or building office where you live!