I realize this is quite correct as far as the NEC, but the logic of it escapes me.
I don't see how a 15-amp receptacle on a 20-amp circuit is a safety hazard. What am I missing?
As long as there are more than one receptacle then 15 amp devices on a 20 amp circuit is permissible per the NEC. Look at the receptacles in your ktchen and bath