50A receptacle on 40A circuit okay?

Users who are viewing this thread

Taylor

New Member
Messages
145
Reaction score
0
Points
0
Location
Northern Joisey
Ok to put 50A receptacle on a 40A circuit, #8 wire? My understanding is that NEC allows derating of 50A range on the belief that normally one will not have all rings and ovens going at once. And #6 wire is a PITA hooking up to a receptacle in a junction box.....
 

Cookie

.
Messages
5,580
Reaction score
8
Points
0
Location
Home
The Amps that the fixture will draw are found on the rating plate on the fixture. Use the corresponding outlet wire and breaker required for the fixture.
 

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
I've never seen a 40 amp range receptacle. But like Cookie says, what is critical is what the load requires.

Nearly all residential ranges require only a 40 amp circuit.

40 and 50 amp breaker/circuit are basically interchangable. You can use either for a 50 amp receptacle.
 

Taylor

New Member
Messages
145
Reaction score
0
Points
0
Location
Northern Joisey
Thanks all. Rex Cauldwell's Wiring for Pros says that NEC allows derating a 50A range to 40A on the basis that homeowners will never have everything on on the range. So you would run #8 wire from a 40A circuit to a 50A receptacle and plug in a 50A range.

Cauldwell disagrees with NEC on this, but having tried to wire up a receptacle on #6 wire in a junction box, I can understand why this might be useful.

In my case, I am looking at a 40A dual fuel range. I was interested in up-sizing for future needs, until I tried it. Just wanted to make sure I did not have to replace the receptacle.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
Any household cooking appliance rated 12kW or less can be used on a 40A circuit.
Also, to answer the original question, yes, a 50A receptacle can be used on a 40A circuit wires with #8. 40A receptacles do not exist.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
THe amp rating of the receptacle is immaterial. The circuit breaker size is determined by the wire, and as long as those two are proper, you can put any recepacle you want on the end of it. IF you overload the circuit, it will trip the circuit breaker, and that is its function.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
THe amp rating of the receptacle is immaterial. The circuit breaker size is determined by the wire, and as long as those two are proper, you can put any recepacle you want on the end of it.
This is not really true. There are strict paramaters as to what receptacles can be used on certain circuits.
See NEC 210.21(B)(1), 210.21(B)(3) and T210.24
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
While it may not happen too often, but imagine that big party when you've really got all the burners on, and the breaker trips when you don't realize it...could make for a nasty end result. While maybe you can, doesn't always mean you should.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
No, I've not seen it happen. But, his dataplate indicates 58A at full draw. It is unlikely that all burners would be on high, but possible. That's a bit over what a 40A circuit should safely support. Most of my personal experience is with gas stoves...some of the newer ones have more burners, and higher wattage than a typical generic stove.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; That's a bit over what a 40A circuit should safely support.

Actually ANYTHING over 40 A, is more than the circuit can safely support, which is WHY the circuit breaker should be sized for the wire, NOT the anticipated load.

That paragraph says that the receptacle cannot be rated LESS than the circuit breaker's capacity, and here is a quote from another area

A 30A receptacle may be placed on a 25A individual branch circuit. As could a 50A receptacle.

Which restates what I said previously.
 
Last edited:

Ian Gills

Senior Robin Hood Guy
Messages
2,743
Reaction score
3
Points
0
Location
USA
You did not say that. You said you could put any receptacle you want on a circuit as long as the breaker and the wire are sized correctly.

You could not put a single 15 amp receptacle on a 20 amp circuit, for example. At least I wouldn't.

Common sense.
 
Last edited:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Just remember.....anything you say after hj has the last word, starts a new thread completely!
 

SteveW

DIY Senior Member
Messages
1,282
Reaction score
22
Points
38
Location
Omaha, NE
You did not say that. You said you could put any receptacle you want on a circuit as long as the breaker and the wire are sized correctly.

You could not put a single 15 amp receptacle on a 20 amp circuit, for example. At least I wouldn't.

Common sense.

I realize this is quite correct as far as the NEC, but the logic of it escapes me.

I don't see how a 15-amp receptacle on a 20-amp circuit is a safety hazard. What am I missing?
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Most receptacles can pass through more current than they can source at an individual outlet and Ian is wrong...you can use 15A devices on a 20A circuit. Although, if you have some one thing that can monopolize the circuit's max current, it's sort of nice to size the outlet for that user.
 

Artie

New Member
Messages
46
Reaction score
0
Points
0
Location
Jacksonville, Fl
For what its worth, twice a year, (Thanksgiving and Christmas), pretty much every burner on the cooktop, and both ovens of the double oven, are going full speed. ;)
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
IN THEORY....a 15 amp equipment could have an internal fault, and since the breaker wouldn't pop until 20, damage or overheating could occur since internally, the equipment is designed to be protected by 15 amps max. This is a stretch of an argument, and the NEC apparently feels comfortable enough to allow it. I do understand that the Canadian Electrical code does NOT allow it.
 