Thread: Bath/Shower Luminaires

  1. #1
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Unhappy Bath/Shower Luminaires

    680.43 Indoor Installations.

    (B) Installation of Luminaires (Lighting Fixtures), Lighting Outlets, and Ceiling-Suspended (Paddle)
    Fans.

    (1) Elevation. Luminaires (lighting fixtures), except as covered in 680.43(B)(2), lighting outlets, and ceiling-suspended (paddle) fans located over the spa or hot tub or within 1.5 m (5 ft) from the inside walls of the spa or hot tub shall comply with the clearances specified in (a), (b), and (c) above the maximum water level.

    (a) Without GFCI. Where no GFCI protection is provided, the mounting height shall be not less than 3.7 m (12 ft).

    (b) With GFCI. Where GFCI protection is provided, the mounting height shall be permitted to be not less than 2.3 m (7 ft 6 in.).

    (c) Below 2.3 m (7 ft 6 in.). Luminaires (lighting fixtures) meeting the requirements of item (1) or

    (2) and protected by a ground-fault circuit interrupter shall be permitted to be installed less than 2.3 m (7 ft 6 in.) over a spa or hot tub.

    (1) Recessed luminaires (fixtures) with a glass or plastic lens, nonmetallic or electrically isolated metal trim, and suitable for use in damp locations

    (2) Surface-mounted luminaires (fixtures) with a glass or plastic globe, a nonmetallic body, or a metallic body isolated from contact, and suitable for use in damp locations
    I need a Philadelphia lawyer to explain to me if it is permissable to mount a surface mount damp location rated luminaire over a tub/shower stall (8' ceiling) GFIC protected?

    Does the fixture (glass lens- metal retaining ring, not sure if isolated from fixture itself) need to be DAMP RATED and/or WET RATED?
    Jack of All Trades...

    ...Master of None...

  2. #2
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    Luminaires installed in/over a tub/shower need to be rated for WET locations if they are "subject to shower spray". You have posted the section of the NEC dealing with spas/hot tubs, which is not the same
    as tub/shower installations. Check out NEC article 410.4.

  3. #3
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Just ignore him he ain't no Philadelphia lawyer he is from Washington although I do agree with him but what do i know i am from NC

  4. #4
    Jack of all trades, Master of none KULTULZ's Avatar
    Join Date
    Nov 2006
    Location
    ROCKVILLE, MD
    Posts
    85

    Thumbs up

    Quote Originally Posted by kreemoweet View Post

    Luminaires installed in/over a tub/shower need to be rated for WET locations if they are "subject to shower spray".

    You have posted the section of the NEC dealing with spas/hot tubs, which is not the same
    as tub/shower installations.

    Check out NEC article 410.4.
    THANX for the reply and I shall...

    Trying to find a suitable surface mount as it is a fire ceiling.
    Jack of All Trades...

    ...Master of None...

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Holy blowtorch, batman! When you think plumbing and electrical codes are obscure...just start into fire codes! NFPA 70, 101, the list goes on as the eyes glaze over.

Similar Threads

  1. Bath/Shower Valve Not Turning Off Bath Water
    By tricky in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 12-16-2007, 08:19 AM
  2. Bath/Shower Valve Not Turning Off Bath Water
    By tricky in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 13
    Last Post: 12-15-2007, 08:41 PM
  3. Bath Fan in Shower
    By robhouston in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 11-13-2007, 08:16 AM
  4. shower over bath: type of bath ?
    By kreid001 in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 03-22-2007, 02:39 PM
  5. converting stand up shower to bath and shower
    By asingletary in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 03-31-2006, 07:24 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •