    Default 3 way switching & fluorescent lights

    First time post- take it easy on me, folks...

    I'm wiring new construction in a garage, and installing 3, 96" fluorescent controlled by 3 way switches. Power source at switch #1, 3 light fixtures, then switch #2. This is a 20A circuit, with 12 gauge wiring throughout.

    I ran 12-3 from switch #1 to the first fixture, then two 12-2 wires between the 3 fixtures, and then 12-3 from the last fixture to switch #2. It worked- I got light, controllable at both ends- but the lights soon started to pulse and flicker slightly.

    After an hour or two, one of the fixtures failed completely (not a bulb problem)- this is the fixture furthest from switch #1 (power source).

    Does this wiring scheme sound appropriate? What would cause the flickering or outright failure? Thanks for any help.

  2. #2

    Default

    The way you have wired the fixtures is incorrect. There is no reason to run the travelers for the 3-ways thru the fixtures. You should have connected power at the first 3-way, run 12-3 between the switches and connected the lights to the 2nd 3-way with one piece of 12-2. You could also connect the lights and power to the same 3-way if that makes more sense. Anyway this is not your problem.

    Your problem could be: 1) The fixtures are not grounded. Fluorescent lights must be grounded for proper operation. 2) Are you using the correct bulbs for the ballast? Just because they fit does not make them the right bulbs! You must cross reference the markings on the ballast with the bulbs. Using higher wattage bulbs than the fixture is rated for can cause flickering or failure to start. (This usually won't damage anything though). Using lower wattage bulbs will overload the ballast and cause it to overheat and fail. 3) The ballasts are bad.

    -rick

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    By any chance is either of the switches a LIGHTED switch, meaning there is a small locator lamp which lights when the main fixture is off??? You can't use that with fluourescents. Also, temperature ( cold ) is an issue with long bulbs, but I assume at this time that is not an issue. A good ground on the fixture IS important.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    All switches do is turn power on or off, and it makes no difference what the power is going to, so if it is an electrical problem we would have to see HOW you wired everything together.

  5. #5
    Light construction, remodelling jjapogee's Avatar
    Join Date
    Sep 2010
    Location
    So. Cal. Mountains
    Posts
    9

    Default

    This is how the fixtures were wired:
    Power to first switch -- 12-2.
    First switch to first light -- 12-3 with white neutral and red/black travelers.
    First light to second light -- One 12-2 is neutral continuing onward and switched hot coming back. Other 12-2 is traveler pair.
    Second light to third light -- Same as preceding.
    Third light to second switch (end) -- 12-3 with red and white travelers, and black for switched hot coming back.

    The wiring scheme must have been correct, since it worked for at least an hour (controllable from either switch)...right?

    After an hour or so, they started to flicker, then one unit failed. The ballasts were VERY hot- the units are virtually suspended between/parallel to rafters (not flush mounted), so there's lots of air movement around them.

    The fixtures are Lithonia T8 MVOLT 120-277v, about $55/ea from the Big Orange Box...could they just be poor quality? (Wouldn't be the first time with HD.) I matched the bulbs properly (32W T8, 48"), according to the fixture's specs.

  6. #6
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Lithonia is top quality. How about the ground on each fixture? Are the switches lighted?

Similar Threads

  1. Motion Sensor and compact fluorescent bulbs
    By paulsiu in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 12-10-2011, 05:39 AM
  2. Stumped by 3 way switching
    By Stephie in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 07-13-2009, 01:23 AM
  3. Seeking 14 1/2" wide fluorescent fixture to fit up between joists
    By AcidWater in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 12-14-2008, 10:38 PM
  4. switching 15-amp to 20-amp (basic Q's)
    By BrownShirt228 in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 09-28-2008, 11:25 AM
  5. fluorescent light bulb's don't work with Timer's?
    By bjferri in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 06-03-2008, 07:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •