    Default Multiple triggers for HVAC fan?

    We have a 2H/2C Honeywell FocusPro 5000 thermostat in our home and it works great most of the time at controlling the temperature. However, our kitchen has several large greenhouse windows, and when the sun is at a certain angle, the solar heat makes the kitchen about 10 degrees hotter than the rest of the house. The existing thermostat doesn't notice this temperature differential because it's located in a different room (near the return duct).

    The way we've always dealt with the hot kitchen has been to go to the thermostat and manually flip the HVAC fan to "on" as this moves the hot air from the kitchen (and presumably, draws it toward the thermostat, which then realizes that the compressor needs to come on to dissipate the heat).

    My question: would it be possible to mount a second basic thermostat in the kitchen that would trigger just the HVAC fan to come on when the kitchen temperature reached a certain level? I'm assuming this is possible as we have a steam humidifier on the furnace that basically does the same thing (turns just the HVAC fan on when steam is being produced). Any tips or tricks on making this work?

    Thanks.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    If you used the fan line as the switched line, it should work. You'd need the 24vac supply line on one terminal, and the fan line on the other and run the thermostat in the cooling mode. Then, when the room got hot, it would connect the 24vac to the fan control line, and turn on the fan.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    You can run any number of t'stats in wired in parallel so that a high temp [=closed contacts] on any of them would run the fan. It's called a wired-OR setup.

Similar Threads

  1. Multiple check valves
    By paullyboy in forum Pumps and Tanks Well Forum & Blog
    Replies: 16
    Last Post: 04-17-2008, 01:39 PM
  2. Washing Machine triggers endless cycling of Pumptrol Pressure Switch
    By Zachrey in forum Pumps and Tanks Well Forum & Blog
    Replies: 15
    Last Post: 02-21-2008, 08:10 PM
  3. Diy Hvac
    By v10rick in forum HVAC Heating & Cooling
    Replies: 10
    Last Post: 07-02-2007, 01:38 PM
  4. Multiple drainings per flush
    By xterra in forum Toilet Forum discussions
    Replies: 4
    Last Post: 06-05-2007, 09:16 AM
  5. Multiple Well Points - help
    By yar02169 in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 05-08-2007, 06:53 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •