    Default PVC Pipe Connected To Metal Drip Pan is Leaking

    Leapin lemurs, we have a big problem. Our central air unit is in the attic. We have a leak where the pvc pipe is attached to the metal drain pan. Why anyone would use metal with pvc is beyond me, but we have to figure out how to fix this. We have a limited budget, and the leak is fairly severe. It is leaking out the ceiling and causing water damaged to our walls also. Any suggestions would be greatly appreciated. Can you adhere plastic to metal?
    Thank you.
    Bright Blessings,
    Gin and Jay

  2. #2

    Default

    It sounds like you are describing your condensate drain and typically, they clog & back up and cause a leak like you are describing. To fix the problem you could just replace the condensate line & if it is 3/4 inch replace it with 1 inch or many times they blow them out with compressed air or similar.

    Hope it works out for you.
    Cookie

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,432

    Default

    You sure the pan isn't just overflowing because of a clog? If you're lucky, something like a coathanger poked down the line will free up the clog. If it IS the pvc, it might have eventually split if it is a female with metal going into it. If you post a picture, someone may be able to give you a good idea how best to fix it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Retired prof. engr. gator37's Avatar
    Join Date
    Nov 2009
    Location
    Alabama
    Posts
    108

    Default

    You have an internal drain pan for and under the cooling coil with piping and P-trap to discharge to the outside (primary drain). You should have another Aux. condensate drain pan under the whole unit that also has a drain or float switch. If you have water in this pan (Aux.condensate drain pan) than you have something clogging your primary drain and P-trap. You should not have any water in the aux drain pan.
    Blow it out with some air or if you are careful with water.

    The other people have answered you primary question about the connection fix

Similar Threads

  1. Toto Soiree Toilet: Drip, Drip, Drip?
    By Philip in Connecticut in forum Toilet Forum discussions
    Replies: 11
    Last Post: 11-16-2013, 10:06 PM
  2. PVC Inside Metal Pipe
    By jandrew in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 05-30-2008, 08:03 PM
  3. How to connect metal pipe to PVC?
    By dereks in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 07-04-2007, 10:36 PM
  4. Drip, Drip, Drip from my shower head
    By miranda12 in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 10-17-2006, 01:49 PM
  5. Metal straps on ABS pipe?
    By David Meiland in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 10-01-2006, 12:39 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •