water heater problems

Users who are viewing this thread

grizzily

New Member
Messages
3
Reaction score
0
Points
0
Location
alabama
installed a 40 gal. hwh soon after tp valve started to leak intermittently. checked to make sure no trash in valve. problem persisted,changed tp valve same problem. installed an expansion tank. city water pressure is static at 70psi,working at 40 psi set tank pressure at70 psi. line pressure still rises to 150 psi and leaks out of tp valve. need help in solving this problem any suggestions helpful
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Until you know WHY the pressure is going that high, and nothing you have told us indicates what the problem could be, there is no way to diagnose it. BUT, one possibility is that you already have a pressure reducing valve and it has gone bad. That would cause your symptoms even with an expansion tank, and a new T&P valve.
 

grizzily

New Member
Messages
3
Reaction score
0
Points
0
Location
alabama
do not have pressure reducing valve. do I need one for 70 psi static pressure to house? before I changed hwh I replaced 1" galv. water pipe with 1/2" cpvc pipe. galv. pipe was almost closed up with build up. could the change in pipe size cause thew problem
 