Thread: Electrician screwed up, what can I do?

  1. #1
    DIY Senior Member ingeborgdot's Avatar
    Join Date
    Mar 2008
    Location
    Kansas
    Posts
    119

    Default Electrician screwed up, what can I do?

    I had new cabinets put in and the electrician came and put in under cabinet puck lighting that had transformers in the cabinet. The wiring is all behind the wall except for the wire running to the pucks. My problem is that the electrician wired 4 20 watt lights to a 12531BK 60 watt transformer. You know what happens next. The lights are rather dim especially compared to the 2 on the right side that are connected to another transformer. These are made by Kichler. What can I do? The cabinets are in and I don't want the guy back. All I need to do is switch to a larger transformer right? If so, does Kichler make an 80 watt transformer? If not, who does and what should I do? Thanks.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    You should contact the electrician and have him correct the problem

  3. #3
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Find a Kichler dealer and ask them what the next size transformer is. Have another electrician install it.
    Answers based on the 2008 & 2011 NEC. If you're on the '14 already I feel sorry for you.

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    The other transformer they make is 180 watts. Just spring for it: http://www.kichler.com/consumer/products/detail/12533BK

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    No matter what you do if you don’t call the original electrician back then you assume all liability of the original installation. Being you said this is a new installation you would lose any warranties written or implied

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    It sounds like this electrician has already "voided" any warranties, if he gave them in the first place.

  7. #7
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    As it stands right now and this is assuming that everything was done correctly the original electrician is bound by law, or at least here in NC, to fulfill the contract and ensure compliant installation. This would include any burden of labor and monies.
    Once the homeowner or anyone else starts working on this installation then the liability of the installation will rest with them.

    All that is required of the homeowner is to contact the electrical inspector and the licensing board and the problem will be resolved in a quick manner.
    If this is one of those deals where the work was being done without inspections then you will in most cases find this type of end result with the added expenses.

  8. #8
    DIY Senior Member ingeborgdot's Avatar
    Join Date
    Mar 2008
    Location
    Kansas
    Posts
    119

    Default

    Ok, can anyone tell me how to fix this problem? I got the 180 w trans/ that the cupboard guy sent me free of charge. I opened up the 180 and actually what is in there is 3 separate trans/. What do I do?//

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Funky situation...that won't help without rewiring things. If all of the leads to the low-voltage lamps come back to one place or you can get them there, you would need to wire two of the transformers to the line voltage, and for the low-voltage side, I'd put two lamps on each. It's fine to under load the transformer. But, a better solution would have been a single transformer, but larger. Maybe they don't actually make one. The safest thing would be to have the electrician fix it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY Senior Member ingeborgdot's Avatar
    Join Date
    Mar 2008
    Location
    Kansas
    Posts
    119

    Default

    Someone said you could splice two transformers to make one. ??????????????????? Will that work?

Similar Threads

  1. Screwed up, now I need to know how bad?
    By Rlogic in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 04-24-2009, 06:44 AM
  2. Think I screwed up
    By apriorius in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 07-11-2008, 09:57 PM
  3. screwed up the bathroom reno
    By plaza500 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 23
    Last Post: 06-18-2007, 08:10 PM
  4. Chipped Porcelain... am I screwed?
    By Randyj in forum Shower & bathtub Forum & Blog
    Replies: 28
    Last Post: 06-05-2007, 01:45 AM
  5. Reasonable, or did I get screwed?
    By BuckWheat in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 26
    Last Post: 03-21-2007, 07:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •