    Please see attached well crafted artistic rendering.

    I ran #12 wire from a 20A breaker to a junction box. From the junction box I created a pigtail and ran to the first GFCI outlet (Line) terminal. Also from the pigtail in the junction box I ran to a second GFCI outlet (Line). Then from the (Load) terminals on those GFCI's I ran to standard 15A receptacles.

    When I switched on the breaker, the first GFCI clicked off and none of the other outlets including the other GFCI outlets were hot.

    So I changed and wired so that the source went to the junction box. From the junction box I ran to only one GFCI (Line). From the (Load) of that GFCI I ran to the (Load) of a second GFCI.

    With that set-up, the first GFCI worked correctly, but none of the other outlets were hot.

    Shouldn't the wiring work as drawn?

    Thanks for any assistance with figuring out this wiring. It seems straight forward enough, but obviously I'm mistaken.
    Attached Images Attached Images  

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    You should be able to feed two branches with GFCI's in them, but why? All you need is one. All receptacles beyond the first one would be protected. No reason to break it into two branches. It's not a good idea to feed one GFCI from another, though (from its load side), but feeding two in parallel to their line sides should work.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3

    Default

    Your hots and neutrals are most likely backwards. The GFI will not reset when they are reversed.
    -rick
    Last edited by drick; 08-09-2010 at 02:05 AM.

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    This should work as drawn. Probably something reversed, or there is additional loads connected on that load side and/or your neutrals are commoned together somewhere creating multiple returns paths.

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by idoc4u View Post
    From the junction box I ran to only one GFCI (Line). From the (Load) of that GFCI I ran to the (Load) of a second GFCI.
    Never connect to the load when supplying a GFCI receptacle.

    The GFCI receptacle will not function should it be supplied to the load end of the device. Never connect to the load when supplying a GFCI receptacle.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,617

    Default

    The way you have it drawn, there should be no way either GFCI would affect the outlets on the other one. Feeding from the load of one GFCI to the load of the other one, turns it into an "junction point", not an outlet. (You could use wire nuts and do the same thing.) BUT, you said "when you turned on the breaker, the GFCI tripped", does that mean it happened automatically, and if so are you sure it was the GFCI and NOT the circuit breaker? If the GFCI did trip when power was supplied to it, then you have a wiring problem, NOT a GFCI one.

  7. #7
    DIY Member idoc4u's Avatar
    Join Date
    Sep 2009
    Location
    Indiana
    Posts
    83

    Default

    hj, both the GFCI and breaker tripped immediately after I switched the breaker on. I must have a wiring issue. I'll have to check it out an be sure that I have it wired as drawn.

    I don't believe joining the neutrals from the breaker box and those going to the "Line" terminals on the GFCI outlets together in the junction box would be incorrect.

    I do have the junction box and outlet boxes grounded.

    I thought I'd solve the problem by taking the hot and neutral from the breaker to the "Line" terminals on just one GFCI outlet and then from the "Load" terminals to my other outlets. When I did this, the downstream outlets didn't work. This suggests to me that I must be wired to the wrong terminals on the GFCI.

    The reason why I wanted to originally use 2 GFCI outlets in parallel was based on the location of the outlets. Wiring this way would be more efficient.

    Thanks again for your input.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,617

    Default

    NO problem with wiring them if "parallel" if the wiring is done correctly. The GFCI will trip because of a fault, the circuit breaker will trip because of a short. The two situations are NOT always, or even usually, the same.

  9. #9
    DIY Member idoc4u's Avatar
    Join Date
    Sep 2009
    Location
    Indiana
    Posts
    83

    Default

    hj, Thanks again for the reply. Here's what happened. I must have had a break in the wire insulation which caused a short. I rewired according to the drawing. My tester showed no power, but neither the breaker nor the GFCI tripped. I plugged in a light and worked like a charm. All outlets tested properly and responded to a manually tripped GFCI. I would not have thought about the tester being bad, but in fact that was part of this issue. Thanks again.

  10. #10
    DIY Member idoc4u's Avatar
    Join Date
    Sep 2009
    Location
    Indiana
    Posts
    83

    Default

    Not that there is any overwhelming reason to do it, but if theoretically wiring 2 GFCI outlets in series, would you wire from the "Load" terminal of GFCI #1 (closest to the breaker) and go into the "Line" terminal of the second?

  11. #11
    Electrical Contractor jbfan74's Avatar
    Join Date
    Jun 2007
    Location
    Newnan, GA
    Posts
    129

    Default

    You could wire it that way, but no reason in the world to do that.
    If ypou felt you needed two gfci receptacles, the you would feed the second one from the line termnals as well as the first one.
    Yes I am A Pirate-Jimmy Buffett

Similar Threads

  1. New GFCI
    By Steven Palmisano in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 05-06-2009, 07:36 PM
  2. gfci won't reset, dead line wires, lights on breaker still work
    By noclue in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 03-16-2009, 10:20 AM
  3. Gfci: Co/alr
    By jimbo in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 10-26-2008, 01:17 PM
  4. AFCI Vs. GFCI
    By Verdeboy in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 12-08-2007, 04:18 PM
  5. Gfci
    By Cat375 in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 08-15-2007, 09:19 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •