    Default pressure and flow problem

    I have a 30 year old system with the original components (submerged pump, well-x-trol wx-202 tank). My problem is that my pressure and flow has been getting worse over the last couple of years. In the last week it has gotten really bad. The pump turns on and fills the tank to 52 psi, it then drains down to 24 psi before restarting. The 1st gallon drains in 42 seconds, 2nd in 52 seconds, 3rd in 57 seconds, 4th in 65 seconds and the last 1/2 gallon took 34 seconds. This means it took 4 minutes 25 seconds to drain 4 1/2 gallons. The plumbing in the house all copper and has no changes, all faucets are affected. Is my problem the pump, tank or pressure switch? We can hardly take a shower. Any suggestions would be greatly appreciated.

    Thanks

  2. #2
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    The important timing is how long to FILL the tank to 52 psi from start at 24 or so. Measure that with no faucets open. If it fills "fast" the pump is ok, and then look for a bad filter somewhere in the system or a broken bladder or diaphragm in your pressure tank that is restricting outflow. Pretty much a certainty that your tank is shot.

    I would set the pressure to 40-60 after you [probably] change the tank.

  3. #3
    DIY Junior Member frank_frc's Avatar
    Join Date
    Aug 2010
    Location
    usa
    Posts
    3

    Default

    The tank is filling in the same amount of time that it has always has. I just cleaned all the screens on the faucets, a little better but not good. If my pressure has been good for 30 years I don't want to change pressure settings.

    Thanks

  4. #4
    Well driller,pump repair. and septic installer Waterwelldude's Avatar
    Join Date
    Feb 2009
    Location
    Texas
    Posts
    303

    Default

    Is there a hose-bib or a valve that is close to the tank you can take apart? Maybe a union at the well itself?

    My bet is that your pipes are almost completely stopped up with minerals. Iron would be my first thought.
    You would need to take a faucet out or brake a union somewhere in the system to check this.

    Might be worth a look.


    Travis
    "I shall never surrender or retreat" -Col. William Travis


  5. #5
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    Alright, 24/52 psi works okay.... You dont give a refill time. If its 30 or 60 seconds, then yes your pipes may have arterial sclerosis or [most likely] your bladder tank has rubber parts blocking the exit of water. Time for a new tank anyway, so start with that.

    I see you have copper pipes. therefore plugged pipes are less likely. I think your tank is shot. Read the 'stickies' at the beginning of this forum

    Pressure tanks DO NOT last 30 years unless they are plain, galvanized. Light a candle at the altar if you get 10 years from a tank.

    [people THINK they have a tank that lasted 20 years, but it was bad for the previous 5 before they checked it]
    Last edited by ballvalve; 08-08-2010 at 11:22 PM.

  6. #6
    DIY Junior Member frank_frc's Avatar
    Join Date
    Aug 2010
    Location
    usa
    Posts
    3

    Default

    I will drain the pressure tank and check to see if it still holds a precharge. That 30 year old tank was probably built in this country by American workers, that's why it's 30 years old. The new tanks are probably built in China, that's why they don't last. It's not that I am cheap, but I need to know what the real problem is. I could replace the pump and tank and still not fix the problem.

    Thanks for your help

  7. #7
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    The name brand tanks are still made here or in canada. They can last a long time if you check them annually even in these days.

Similar Threads

  1. Flow problem
    By estone in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 05-06-2008, 08:18 AM
  2. Do I have a flow problem
    By designsoutdoors in forum Irrigation / Sprinkler Forum
    Replies: 1
    Last Post: 05-04-2008, 10:02 PM
  3. Seems to be a flow problem....
    By DIY in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 04-17-2008, 07:20 AM
  4. Whole house flow problem
    By shag_fu in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-25-2008, 07:01 PM
  5. Low flow problem with hot water tap
    By Wanna Be in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-28-2006, 05:29 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •