    Default pipe size /max length of run for kitchen, Canada Code

    hello
    I have been asked to rough in a new kitchen, it has 1 double sink and a dishwasher beside it, the soil pipe is 25 to 30 feet away, I don't want to run 3 inch all the way if it isnt needed , thanks

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,534

    Default

    Even IF 1 1/2" would be approved, there is no way I would EVER use it for anything other than a vent. I ALWAYS use 2" minimum for my drain lines.

  3. #3
    DIY Junior Member Philbert's Avatar
    Join Date
    Aug 2010
    Location
    Toronto,Ontario,Canada
    Posts
    5

    Default

    the problem I am having is that if I seach online for a quote from the npc I get a vague reference to some "complicated table" in the plumbing code book which I can acces online unless I pay for it or order a copy of the code book for a price of course,if ther is no restriction all the better, although I will likely use 2 inch anyways, ohhh the 25 to 30 foot run is a sloped run not a drop ifin that changes anything

  4. #4
    Moderator and Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,003

    Default

    It is not a "complicated table" at least not in the books down here. Each fixture is desinated by a number which correlates to how much water is likely to go in it. The number is called "fixture units". In the UPC, a kitchen sink is 2 FU. By the simple table, the maximum # of FU on a horizontal 1½" pipe, beyond the trap arm, is ONE. So the sink needs to drain into a 2" lateral. The horizontal length ( with 1/4" per foot slope minimum) is unlimited.

  5. #5
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    812

    Default

    Quote Originally Posted by Philbert View Post
    hello
    I have been asked to rough in a new kitchen, it has 1 double sink and a dishwasher beside it, the soil pipe is 25 to 30 feet away, I don't want to run 3 inch all the way if it isnt needed , thanks
    1.5" is perfectly acceptable as long as you pick up your vent within 6'.

    I usually have a 1.5" fixture drain picked up by a 2x1.5x1.5" tee.

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    12,427
    Blog Entries
    1

    Default

    I haven't seen 1.5 for kitchens since the 50's in the lower 48, not Canada though.
    Here we use 2" until the vent, and then a 1.5" trap arm.

    I guess the Canadian code for kitchen plumbing is pretty weak.

  7. #7
    Certified Plumber Plumber1979's Avatar
    Join Date
    Jul 2012
    Location
    Ontario
    Posts
    16

    Default

    im a plumber here in Ontario and its just fine to use 1 1/2 on a kitchen and it 5' for the vent

  8. #8

    Default

    1-1/2" is fine. trap arm max is 5' (1.5m). cleanout required on fixture drain or union p-trap. cleanouts every 20' (6m).. you'll want to make sure your slope is right to keep a kitchen sink line that long, clear of grease etc.
    secondly NPC is not what you need. you need to refer to the Ontario Building Code section 7 - Plumbing

Similar Threads

  1. Laundry drain pipe help for s-trap location. Canada
    By klrman in forum Canadian Plumbing Code Questions
    Replies: 11
    Last Post: 06-03-2010, 02:40 PM
  2. Laundry drain pipe help for s-trap location, Canada
    By klrman in forum Plumbing Forum Discussion & Blog
    Replies: 11
    Last Post: 06-03-2010, 02:40 PM
  3. Typical drain pipe size for IPC code?
    By Mudball in forum Plumbing Forum Discussion & Blog
    Replies: 18
    Last Post: 08-24-2009, 06:22 AM
  4. IPC Code: Main line and Venting size
    By construct30 in forum Plumbing Forum Discussion & Blog
    Replies: 0
    Last Post: 12-05-2007, 05:21 PM
  5. Matching pump h.p. to well point size and length?
    By ron in sc in forum Pumps and Tanks Well Forum & Blog
    Replies: 11
    Last Post: 06-06-2007, 05:52 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •