    Default Water Heater Inspection - Drain Valve Angle Question

    The water heater drain valve angles about 2 inches up hill from the water heater to the wall, the inspector said this is an issue and safety hazard. How concerned should we be able this? Below is a picture

    We want to have it fixed if it is a major issue, however, if we shouldn't be concerned I don't want to force them to change it. Thanks

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,209
    Blog Entries
    1

    Default

    Cut the wall and lower the 90 in the wall.

    Below is my favorite exploding water heater video.
    In the Seattle area, a water heater shot though a garage roof and landed blocks away.



  3. #3
    In the Trades jnaas2's Avatar
    Join Date
    Mar 2009
    Location
    Evansville In
    Posts
    76

    Default

    where is the line going to

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    It is a fairly serious problem. Almost guaranteed that as time goes by, some drippage will occur from the valve, or some condensation will occur in the line. This water will sit right there at the relief and leave mineral deposits, clogging the valve. It might not work when it needs to.

    Somewhat shocking that it is done this way.....obviously no permit because the inspector would still be looking for a big enough crayon to write NO WAY.....all over the papers!

  5. #5
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    It is a definite FAIL...

    It will cause the reliability of the T&P valve to suffer and could result in a hazardous condition....

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,673

    Default

    The easiest way to correct it is to place some concrete blocks, or a few circular concrete stepstones, under the heater to raise the valve above the opening in the wall. That corrugated connector is also "illegal" in most areas. Use copper tubing to connect the SAFETY valve, (not a DRAIN valve), to the pipe at the wall. In Phoenix, the heater landed a block away, and the house had to be demolished because it was not repairable.
    Last edited by hj; 07-24-2010 at 09:21 AM.

  7. #7
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,463

    Default

    Sorry to see that you have a Whirlpool Energy Smart water heater as well....

Similar Threads

  1. Low pressure electric water heater after sprinkler inspection
    By randy Boston in forum Water Heater Forum, Tanks
    Replies: 10
    Last Post: 11-04-2009, 07:24 PM
  2. Water heater inspection...
    By thinkly in forum Water Heater Forum, Tanks
    Replies: 18
    Last Post: 05-29-2009, 11:40 AM
  3. neo angle shower drain question
    By johnnyhomeowner in forum Shower & bathtub Forum & Blog
    Replies: 4
    Last Post: 04-24-2008, 04:51 AM
  4. Question on planning for inspection and floor drain
    By camerono in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 11-07-2006, 10:25 AM
  5. direct-vent gas-fired water heater inspection.
    By canton in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-05-2006, 02:53 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •