Thread: Shared up-the-wall vent for three fixtures?

  1. #1
    DIY Junior Member rossow (mn)'s Avatar
    Join Date
    Jul 2010
    Location
    Minnesota
    Posts
    5

    Default Shared up-the-wall vent for three fixtures?

    I'm turning a 5x9 porch (over shallow crawl space) into a three-quarter bath with lavatory on east wall, shower across south end, toilet on west wall. I'd like to bring the lavatory drain and shower drain together into a 2" wye, then that wye into the two-inch wye neck of a 3x3x2 fitting that will aim toward my 4" main drainline in the basement. The lav/shower drain would enter the 3" main line a foot or so downstream of the closet bend. All the drains will be horizontal (lying under the subfloor) with proper 1/4" drop per foot until the 3" drops vertically into the 4" basement plumbing. My question is regarding venting. With such short drain lines (nothing more than five feet apart) can I get by with one 2" vent in a wall (either for the lavatory or toilet) serving all three fixtures, or do I need separate vents for each? The vent could go straight up through the roof on either the lav wall or the toilet wall. In other words, do I need three pipes up a wall or will the one 2" vent pipe that joins the drain under the floor be sufficient to vent all three fixtures? I know it is OK to run separate vents for each fixture upward to join one large through-the-roof vent above the ceiling; what I'm asking is whether I can avoid two of those three pipes going up a wall. Is this at all clear what I'm explaining? FWIW, there are no codes or inspections or permits required; I'm in an area where no one officially cares, but I try to do work that would meet typical codes. Thanks for any advice.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    VEnt requirements have NOTHING to do with how close the fixtures are to each other. IT depends on HOW the piping is arranged. From YOUR description, and that is all we have to go by, it is a proper installation, IF you actually install it the way you indicate. Depending on the actual space limitations, however, I might do it completely differently.

  3. #3
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    Done properly you can wet vent the entire bath group though a single 2" vent
    Perception is 3/4 of reality

  4. #4
    DIY Junior Member mnzpasquale's Avatar
    Join Date
    Jul 2010
    Location
    New York
    Posts
    8

    Default

    Is this what u are trying to describe ???
    Attached Images Attached Images  

  5. #5
    DIY Junior Member rossow (mn)'s Avatar
    Join Date
    Jul 2010
    Location
    Minnesota
    Posts
    5

    Default

    Yes, that's one possibility. The other would be to have the vent on the west wall, just downstream of the WC bend. Would your illustration work? Thanks for offering it.

  6. #6
    DIY Junior Member mnzpasquale's Avatar
    Join Date
    Jul 2010
    Location
    New York
    Posts
    8

    Default

    I was just trying to get a picture of what u were saying...as for what will work...u need to take advice from Hj , or Wally, they are the pros...I just thought a illustration could help with discussion...

  7. #7
    DIY Junior Member rossow (mn)'s Avatar
    Join Date
    Jul 2010
    Location
    Minnesota
    Posts
    5

    Default

    Thanks. I'll be hoping they reply regarding your sketch.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    His should work, always assuming you install it as shown. Your suggestion would not, however. The lavatory vent as shown would HAVE to be installed. Any other vents might be superfluous or redundant.

Similar Threads

  1. vent through a wall
    By Esquire in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 06-01-2010, 07:09 AM
  2. Heat vent on the shower Wall
    By yomero in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 09-28-2009, 05:57 PM
  3. Vent termination: above roof -vs- out the wall
    By Carradine in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-08-2009, 05:54 PM
  4. AAV vent & trap in wall
    By Alpac in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 03-30-2008, 11:30 AM
  5. Shared vent-exhaust stack
    By gmilton in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 04-19-2006, 10:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •