Thread: Electrical - Dishwasher hookup.

  1. #16
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by ActionDave View Post
    Why?
    It has a motor for the pump therefore it must comply with 422.32 with a means to disconnect in-sight of the appliance. It must also comply with part 9 of 430

  2. #17
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    Going to disagree with you Mike.

    (B) Appliances Rated Over 300 Volt-Amperes or 1⁄8
    Horsepower. For permanently connected appliances rated
    over 300 volt-amperes or 1⁄8 hp, the branch-circuit switch or
    circuit breaker shall be permitted to serve as the disconnecting
    means where the switch or circuit breaker is within
    sight from the appliance or is capable of being locked in the
    open position.
    The provision for locking or adding a lock to
    the disconnecting means....

  3. #18
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Jim Port View Post
    Going to disagree with you Mike.

    (B) Appliances Rated Over 300 Volt-Amperes or 1⁄8
    Horsepower. For permanently connected appliances rated
    over 300 volt-amperes or 1⁄8 hp, the branch-circuit switch or
    circuit breaker shall be permitted to serve as the disconnecting
    means where the switch or circuit breaker is within
    sight from the appliance or is capable of being locked in the
    open position.
    The provision for locking or adding a lock to
    the disconnecting means....
    Brother Jim look down one more code section and find this one;

    422.32 Disconnecting Means for Motor-Driven Appliance.
    If a switch or circuit breaker serves as the disconnecting means for a permanently connected motor-driven appliance of more than 1⁄8 hp, it shall be located within sight from the motor controller and shall comply with Part IX of Article 430.
    Exception: If a motor-driven appliance of more than 1⁄8 hp is provided with a unit switch that complies with 422.34(A), (B), (C), or (D), the switch or circuit breaker serving as the other disconnecting means shall be permitted to be out of sight from the motor controller.

    What you posted was for an appliance that does not have a motor. Just because something is rated in horse power does not mean it is a motor. Look at motor controllers. They are rated in horse power but the only control the motor. Check out the rating of this switch

    http://www.intermatic.com/products/t...ers/st01c.aspx

    This switch is not a motor but it is rated at 1 hp at 120 volts and 2 hp at 240 volts

    here is a motor stater that is "rated" in horse power but there is no motor
    http://www.pacificex.com.au/pdf/PEX-...-0112-0112.pdf

    The section you posted is for appliances of over 300 watts or that are rated over one eighth horse power. There in nothing in that section that concerns motors. Appliances with motors is one more section down

    Here is a section concerning energy savings. Look at how they have rated the airconditioners

    Energy ratings system
    The familiar yellow stickers with energy ratings stars that appear on major electrical household appliances are a legal requirement across Australia. Energy labels are a government service designed to inform consumers about energy consumption. They are mandatory on the following appliances:

    Refrigerators and freezers
    Clothes washers
    Clothes dryers
    Dishwashers
    Airconditioners
    The star rating is calculated on how efficient a product is, not just how much energy it uses. For example, a 3.5 horsepower airconditioner will use more energy than a 1 horsepower airconditioner. But the larger airconditioner will have a higher rating if it uses the energy in a more effective way.

    As one can see the airconditioners are not rated in tonage but instead rated in horse power.
    In the lab one horse power is equal to 746 watts of electrical energy.
    Last edited by jwelectric; 07-20-2010 at 12:05 PM.

  4. #19
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    I can see your point, however a DW and disposal are specifically mentioned in 422. It is also how that requirement is enforced here.

    IMO 430 is not dealing with these type of motors in appliances.

  5. #20
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by Jim Port View Post
    I can see your point, however a DW and disposal are specifically mentioned in 422. It is also how that requirement is enforced here.

    IMO 430 is not dealing with these type of motors in appliances.
    422.32 Disconnecting Means for Motor-Driven Appliance.
    If a switch or circuit breaker serves as the disconnecting means for a permanently connected motor-driven appliance of more than 1⁄8 hp, it shall be located within sight from the motor controller and shall comply with Part IX of Article 430.
    Exception: If a motor-driven appliance of more than 1⁄8 hp is provided with a unit switch that complies with 422.34(A), (B), (C), or (D), the switch or circuit breaker serving as the other disconnecting means shall be permitted to be out of sight from the motor controller.

    Yes the dishwasher is an appliance where a motor is driving the pump which operates the appliance therefore the section of 422 outlined above applies

    By the way, just because something is enforced that way does not make it correcr

  6. #21

    Default

    Hi all, am reviving this old thread since it pertains to exactly what I am doing.

    If I am reading it correctly it is permissible to connect a DW via a correctly sized cord with a plug, and plug it into an outlet in an adjacent cabinet - in this case the sink base, or in an outlet mounted in the wall with the rear of the cabinet cut out for access to the outlet.

    If I chose to surface mount a box to the inside of the cabinet is it permissible to simply bring the feed wire through a hole in the drywall and cooresponding hole in the cabinet (this seems like an inelegant way of doing things).

    Same question pertains to the garbage disposal - can I also connect it to an outlet via cord and plug, or must it be hard wired?

    Finally, must the dishwasher and disposal be on completely seperate circuits?

    Many thanks,

    Dan
    If I remember correctly, my memory is excellent, but my ability to access it is not.

  7. #22
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Yes
    Yes
    Maybe but most likely yes

  8. #23

    Default

    Many thanks!

    Dan
    If I remember correctly, my memory is excellent, but my ability to access it is not.

  9. #24
    DIY Senior Member Chad Schloss's Avatar
    Join Date
    Jun 2010
    Location
    USA
    Posts
    327

    Default

    Can you have a dishwasher hardwired, but then have the 14/2 for the d/w run to a junction box, say in a crawlspace or basement, where it then ties into a short cord to be plugged into a receptacle (under the sink, for means of disconnecting)?

  10. #25
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by Chad Schloss View Post
    Can you have a dishwasher hardwired, but then have the 14/2 for the d/w run to a junction box, say in a crawlspace or basement, where it then ties into a short cord to be plugged into a receptacle (under the sink, for means of disconnecting)?

    I cannot for the life of me imagine why one would. I cannot cite the code restriction, but I am as certain as I can be that one cannot have a cord disappear into a wall or a floor.

    Why not just run MC from the DW to a switch box in the sink cabinet?

  11. #26

    Default

    Thanks for the additional replies.

    One of the reasons for the ask is that this DW, a Bosch unit, has the electrical connection at the bottom front of the unit and the feed then runs down, under, and back through a channel in the bottom of the enclosure (ditto with the water line - but through it's own channel). The J-box at the bottom front is extremely small and trying to stuff 12 or 14/2 into it is no picnic. Using a cord/plug would allow me to wire into the J-box with more flexible wire, lay the wire into the channel, feed the electrical, water, and drain lines throught the sink base cab.

    Anyway, I've got it squared away - terminated a dedicated circuit in a wall box with a duplex receptacle within the sink base cabinet. I have a second dedicated circuit in the same box for the garbage disposal. Had I thought it out a little more I could have gotten away with one receptacle for both but as it now stands only one outlet on each is live.

    Dan
    If I remember correctly, my memory is excellent, but my ability to access it is not.

  12. #27
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by ss3964spd View Post

    Anyway, I've got it squared away - terminated a dedicated circuit in a wall box with a duplex receptacle within the sink base cabinet. I have a second dedicated circuit in the same box for the garbage disposal. Had I thought it out a little more I could have gotten away with one receptacle for both but as it now stands only one outlet on each is live.

    Dan
    Not to be pedantic or make you miserable, but:

    A dedicated circuit for a single appliance is supposed to end in a single outlet, not a duplex.

    As you describe, you could have had a duplex with the two receptacles used for the two circuits.

    In that event, it is required that they be feed in common by a two pole breaker, such that if one circuit trips, both will go cold. I really need to retrofit the one in my kitchen.....

    And of course one uses one neutral conductor, as the two circuits will be at opposite ends of the phase. One does not use one length of NM to bring one hot and one neutral and another to bring another neutral.

    This gets so very complicated......you have only violated a small item in the code (using two duplex outlets to terminate two dedicated circuits), there are aspects of the code that are harder to explain than others. This might be one of them.

  13. #28

    Default

    No worries, Burb, I like to learn and do things as correctly as I can.

    Maybe my explanation wasn't clear. I have two completely seperate circuits, both feeding into a single 2 gang box. Although I used two duplex receptacles I broke off the connecting tabs on each side of both receptacles, effectively rendering them (in my mind anyway) 4 single receptacles. The DW circuit is connected to the top of the duplex, the bottom is dead. Same for the BD. Once the DW and GD are plugged into their dedicated receptacle I didn't want anyone to plug anything else in so the others are dead. The only thing common is the 4 gang box. Does this arrangement seem sound or is it still a little wonky?

    What I meant by "I could have gotten away with one receptacle for both" was I thought I could have broken the side tabs off one duplex receptacle and wired one circuit to the top and the other to the bottom. I'd still have two separate, dedicated, circuits, sharing only the plastic body of the duplex receptacle.

    Dan
    If I remember correctly, my memory is excellent, but my ability to access it is not.

  14. #29
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by ss3964spd View Post
    No worries, Burb, I like to learn and do things as correctly as I can.

    Maybe my explanation wasn't clear. I have two completely seperate circuits, both feeding into a single 2 gang box. Although I used two duplex receptacles I broke off the connecting tabs on each side of both receptacles, effectively rendering them (in my mind anyway) 4 single receptacles. The DW circuit is connected to the top of the duplex, the bottom is dead. Same for the BD. Once the DW and GD are plugged into their dedicated receptacle I didn't want anyone to plug anything else in so the others are dead. The only thing common is the 4 gang box. Does this arrangement seem sound or is it still a little wonky?

    What I meant by "I could have gotten away with one receptacle for both" was I thought I could have broken the side tabs off one duplex receptacle and wired one circuit to the top and the other to the bottom. I'd still have two separate, dedicated, circuits, sharing only the plastic body of the duplex receptacle.

    Dan
    What you have done is extremely dangerous.

    You have a duplex receptacle, two in fact, where half of the receptacle is unpowered.

    A repairman could easily get under there and think he has turned the power off and not actually have done so.

    You should reverse what you did. To be fully to code, replace the two duplex receptacles with single receptacles. If you just want to use duplexes, that would be much safer than what you did.

    Or change it to one duplex with two hots, opposite sides of the phase, fed by a two pole breaker.

    If the neutrals for the two hots are taking different routes (not a shared three-wire circuit) then break the tab on the neutral side as well and be VERY aware of which neutral goes with which hot. I'd tape them together a few inches behind the receptacle, color coded.

    The first solution is the best, considering that you have a two gang box. Getting a faceplate to suit might be a pain in the back side.
    Last edited by Homeownerinburb; 06-26-2012 at 04:55 PM.

  15. #30

    Default

    Quote Originally Posted by Homeownerinburb View Post
    What you have done is extremely dangerous.

    You have a duplex receptacle, two in fact, where half of the receptacle is unpowered.

    A repairman could easily get under there and think he has turned the power off and not actually have done so.
    Thank you for that insight. I always build/work to code (which is why I wanted to bounce this off the folks here) but since I do all my own work I often forget that eventually someone other than me might end up having to deal with something.

    Thanks Burb, I'll go back and make it right.

    Dan
    If I remember correctly, my memory is excellent, but my ability to access it is not.

Similar Threads

  1. Washer hookup electrical outlet box
    By DIY in forum Electrical Forum discussion & Blog
    Replies: 17
    Last Post: 06-28-2010, 09:43 AM
  2. Dishwasher Hookup Help
    By freshmo55 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 10-20-2009, 11:45 AM
  3. Electrical Engineer allowed to do Electrical work?
    By willijimon in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 03-05-2009, 05:08 PM
  4. Can I hookup a dishwasher here?
    By jeffesonm in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-05-2009, 05:21 AM
  5. Dishwasher Air Gap hookup size mismatch?
    By stinkyDavis in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 11-27-2006, 03:22 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •