    Default In-Line Vent vs. Air Admittance Valve?

    What is the differnece between these two, and what is the recommended use for an S trap in a basement lav? I am looking at the Oatey 3901 In-Line and the Oatey 39016 AAV if that helps..... Thanks!!

  2. #2
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    If you have a S trap there is no point in venting it anyway.
    Perception is 3/4 of reality

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    The 3901 is just an air admittance valve, el cheaop version. Make sure if you put on ANY aav that it is installed vertically.

  4. #4
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    Where would you put a vent on an S trap that would make any difference. If you vent the lateral that it dumps into it still has no effect on the S trap siphoning. If you put it at the only place that would prevent siphioning, which would be the crown of the trap, then you have an illegal crown vent.
    Perception is 3/4 of reality

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    They are essentially the same, regardless of what they call them. You CANNOT vent a true "S" trap. You can only use an AAV to keep a "P" trap from becoming an "S" trap.

  6. #6
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    S straps are illegal under every code, the reason being, they are not vented.

  7. #7
    DIY Junior Member dzd9fy's Avatar
    Join Date
    Dec 2006
    Location
    Michigan
    Posts
    26

    Default

    Ok, thanks for the clarification on the differences between the two.

    I am a bit confused on the comments that since it is an S trap it cannot be used, so looking for some insight here. Given the trap is where it is, has worked well for the past 10 years we have been here and guessing since the house was built [1950], what is the suggestion since this is burried under the cement?

    Also, how and why would one use this valve vertically on a P trap? That makes absolutely no sense to me....

  8. #8
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    S traps used to be used, but are very prone to the trap siphoning dry, so are not allowed today. To install the aav, you could possilby santee off the vertical, turn up with an elbow, and put the aac there. Being below the flood rim, this could be problematic. Maybe a wye and a 45 to take if vertical? I would be interested in an inspectors take on this,

  9. #9
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    The only way to do it and be compliant would be to come vertical out of the floor into a sanitary tee with the aav on top of the tee and a P trap into the fixture. As long as the S trap remains there is no code compliant way to vent it.
    Perception is 3/4 of reality

  10. #10
    DIY Junior Member dzd9fy's Avatar
    Join Date
    Dec 2006
    Location
    Michigan
    Posts
    26

    Default

    ok..... so should I just leave well enough alone? It has been working fine, I was just thinking this would be something that would be a good improvement to a less than ideal, and now not permitted use.

    Thanks guys!

  11. #11
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    Yep, let it be. If you notice any odor, run a bit of water in the sink. called priming the trap in the old days.
    Perception is 3/4 of reality

Similar Threads

  1. Air admittance valve on sewage pump?
    By klpellam in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 07-22-2009, 07:06 AM
  2. Ejector Pump Box with Air Admittance Valve (LONG)
    By ak199 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 52
    Last Post: 01-09-2009, 04:58 AM
  3. Air admittance valve - "above the flood level rim"?
    By schmeel in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 07-26-2007, 07:52 PM
  4. Can I vent New bathroom vent into dryer vent line?
    By cwolters in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 04-25-2005, 04:03 PM
  5. Air Admittance Valve
    By Barry in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 04-25-2005, 11:07 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •