Results 1 to 5 of 5
Thread: WC venting, UPC code
    DIY Senior Member DavidTu's Avatar
    Dec 2009
    Seattle, WA
    Default WC venting, UPC code
    I have the following situation for a WC (see pics)... the WC is dropping to a closet bend then going down for around 1ft at 45-deg... I can vent it either on the 45-deg drop (so about 10" below WC) or after it levels out (around 14" drop from the WC). I cannot vent before dropping down b/c there is a chimney in the way and I must turn and drop right away.
    Normally, for a fixture the vent take-off must be above the p-trap weir; in a WC of course that is not possible... but I am wondering what the acceptable limits are... or how far can I drop below WC closet flange before venting?
    So am I ok with alternative #1 or #2 (see pics) or must I do something else?
    For the water closet, either would be fine. It needs to be a wye or combo fitting on the vent.
    For a water closet, you could even have taken it off the vertical with a wye. In King county, the vent should be within six feet of the flange.
    Either will be fine, but if the inspector is one who only reads the book, but does not know WHY it is in the book, he may have a problem with it.
    The Seattle inspectors are good. I don't see a problem.
    Dec 2009
    Seattle, WA
    Thanks much!
  1. Vet my Venting please? IPC code
    By RoseHawke in forum IPC Plumbing Code Questions
    Last Post: 02-26-2011, 04:43 PM
  2. Venting Under a Porch-National Code Reference
    By Noth Jersey in forum Plumbing Forum Discussion & Blog
    Last Post: 10-08-2009, 06:14 AM
  3. Code for Dryer Venting
    By molo in forum HVAC Heating & Cooling
    Last Post: 09-24-2009, 05:35 AM
  4. Code for Dryer Venting: Part II
    Last Post: 09-21-2009, 05:42 PM
  5. IPC Code: Main line and Venting size
    By construct30 in forum Plumbing Forum Discussion & Blog
    Last Post: 12-05-2007, 05:21 PM