Results 1 to 7 of 7

Thread: critical distances, UPC

  1. #1
    DIY Junior Member 69gtocv's Avatar
    Join Date
    Jun 2010
    Location
    Spokane, Wa
    Posts
    23

    Default critical distances, UPC

    As the title says, looking for info on what is actually measured to determine those. Check out the drawing.

    Also, UPC is used where I'm building this house. My drain line to the septic tank from the house is 4". I know my total cross sections of all my vents must equal or exceed that of the 4". From the drawing you can see I'm using 2" for my vent from the lavs, but will increase it to 3" before it exits out the roof to help keep it open in winter conditions. So for my total vent calculations, can I use 3" for that vent or do I have to use 2" since that vent is that size for the majority of its run?

    Thanks, Jeff
    Attached Images Attached Images  

  2. #2
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    All distances are critical.
    Perception is 3/4 of reality

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    With UPC,

    1.5" lines vented within 42"
    2" lines vented within 60"
    3" lines vented within 72"

  4. #4
    DIY Junior Member 69gtocv's Avatar
    Join Date
    Jun 2010
    Location
    Spokane, Wa
    Posts
    23

    Default

    Quote Originally Posted by Terry View Post
    With UPC,

    1.5" lines vented within 42"
    2" lines vented within 60"
    3" lines vented within 72"
    Thanks, I'm aware of the actual maximum dimensions, my question was whether the lines marked in red in my drawing were where you actually took the measurements from (the horizontal lines only) or do you also have to add the vertical measurement from horizontal until the vent actually takes off from above the double fixture fitting?

    And any idea on the 2nd question?

    Thanks, Jeff

  5. #5
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    If I'm not mistaken, you will only measure to the wye on the horizontal (where the two lavs tie into the tub line). This is where your wet vent effectively starts.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    The tub's "critical distance" is from the trap to the point where the sink drain connects, and the toilet's is from the opening to the connection with the sink/tub drain. At those points, the sink's drain becomes the wet vent for those two fixtures.

  7. #7
    DIY Junior Member 69gtocv's Avatar
    Join Date
    Jun 2010
    Location
    Spokane, Wa
    Posts
    23

    Default

    Quote Originally Posted by hj View Post
    The tub's "critical distance" is from the trap to the point where the sink drain connects, and the toilet's is from the opening to the connection with the sink/tub drain. At those points, the sink's drain becomes the wet vent for those two fixtures.
    Thank you. I was concerned I had to count the distance back to where the vertical comes down as well. I'll be fine now.

Similar Threads

  1. How critical is valve to spout measurement?
    By jadnashua in forum Shower & bathtub Forum & Blog
    Replies: 4
    Last Post: 05-13-2010, 09:32 PM
  2. Spa tub vent critical distance
    By fecollier in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 01-27-2010, 08:13 AM
  3. Pipe sizes for drain, vent, and distances for Colorado Springs, Colorado
    By avtinc2000 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-03-2006, 04:10 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •