    Default Would be thankfull for some advice...waste stack ques.

    Hi Guys, first hav to say really like the site, its great...
    Heres my problem, I am adding small powder room and need advice on connecting to main stack.
    Layout is done, everything vented and proper pipe sizes,,, just want opinions on best way to connect to main stack. I got my diamond torch blades ready for cutting but I am not sure if a wye or tee fitting would work best? And how to drop down the last 3' within a 4' span?
    I am going to hopefully include a rough drawing with this post ( I'm new so I hope I can do it)...

    New York State Code
    Attached Images Attached Images  
    Last edited by Terry; 07-02-2010 at 11:21 AM.

  2. #2
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    a sanitary Tee is always the preferred fitting for joining to a vertical stack.
    Perception is 3/4 of reality

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    WHO said the new piping is correct? If this is a vertical stack, then a "Y" with the branch rising up to a 45 which then levels the pipe out to meet your connection.

  4. #4
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    Good point but I have no clue what is above or what the new piping will look like.
    Perception is 3/4 of reality

  5. #5
    DIY Junior Member mnzpasquale's Avatar
    Join Date
    Jul 2010
    Location
    New York
    Posts
    8

    Default

    Thanks for reply guys... I am thankfull for your advice... sorry for confusion, I thought showing the joists would show it is a vertical stack, other info I should include is that I am only adding toilet, sink was existing... I was able to place wye within 4' of toilet drain for 2" vent that goes to attic and connects to existing vent ( I made sure to roll wye and go 45 vertical into wall as not to hav flat vent as u guys always advise against) so really my question is just about connecting 3" to 4" cast iron vertical stack. Is this new pic. what u guys mean? I used 45 elbows (2) to drop below joist because someone said it is better flow. I am just trying to get plan...hoping u guys can advise me on whats best and correct...thanks again.
    Attached Images Attached Images   

  6. #6
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    631
    Blog Entries
    1

    Default

    Where is your vent line coming off that 3" waste before 4" stack ?

    MACPLUMB 777

    E-MAIL
    JERRYMAC@TROJANWORLDWIDE.COM


    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER
    AND BOILERS SINCE JAN, 1989

    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT
    Trojan Worldwide Web Site


     



  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    IT looks like it will work, although if I were doing it, I would have used a 45 and a 60 degree fitting to make a "rolling 45 angle rather than two 45s and a 90 combination.

  8. #8
    DIY Junior Member mnzpasquale's Avatar
    Join Date
    Jul 2010
    Location
    New York
    Posts
    8

    Default

    Thanks HJ.. I will do it like u suggest...I trust your advice is the better way

    To answer Mac, my vent is about 3' from flange, I rolled wye coming 45 up to wall then straight up to attic connecting with existing roof vent.

  9. #9
    DIY Junior Member mnzpasquale's Avatar
    Join Date
    Jul 2010
    Location
    New York
    Posts
    8

    Default

    Again thanks for the comments...really do want as much advice as you guys can give, this is all theory right now as I havent glued anything, just dry fit... so more advice is welcome

Similar Threads

  1. Waste Stack
    By ptomt77 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 05-13-2010, 12:31 PM
  2. Leaking Waste Drain Stack
    By Duke76 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 09-18-2009, 05:56 AM
  3. Bathtub drain PVC to ABS waste stack
    By woods1966 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-18-2009, 12:23 PM
  4. PVC drain into ABS waste stack
    By stonypaw in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 05-14-2008, 09:47 AM
  5. Re-routing a waste stack branch line
    By rrzepka in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 12-11-2004, 08:14 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •