    Default Another Bryant Evolution Question

    Today I had installed in my home a Bryant 355 CAV furnace, 187BNA 036-A Air handler, and an Evolution control system.
    My question is when I change the fan speed at the thermostat, shouldn't at some point the fan motor run faster or slower depending on the setting? No matter where it is set, (low, medium, high, or auto) the fan motor remains constant. And there is no change in the amount of air being pushed out of the duct work. Is it possible the wiring was done wrong? The house won't cool down below 77 deg. The contractor only says "you gotta give the equipment 48 to 72 hrs. to remove the humidity."
    I'm confused and HOT!
    Any help would be greatly appreciated.
    Last edited by turkinpa; 07-09-2010 at 06:39 PM.

  2. #2
    DIY Member Lightwave's Avatar
    Join Date
    Aug 2007
    Location
    Vancouver, BC
    Posts
    98

    Default

    The fan speed button on the Evolution thermostat sets fan speed for when the system is idle. Fan speed is set by the thermostat (without any user adjustment options) when the system is heating or cooling.

    Evolution control wiring is largely 'all or nothing.' Miswiring won't cause malfunctions; it will prevent the system from working at all.

    As far as not cooling below 77, how hot was your house before this system was installed? If you had indoor and outdoor temperatures over 100, it will take a while (a day or more) to draw down indoor conditions to something tolerable. If, on the other hand, you've had the system for a few days and/or had livable conditions inside before turning on the AC, then there's probably something wrong.

Similar Threads

  1. Bryant Evolution Question
    By moisheh in forum HVAC Heating & Cooling
    Replies: 8
    Last Post: 06-08-2010, 12:24 PM
  2. InSinkErator Evolution Septic Assist
    By Dysrhythmic in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-07-2009, 08:17 AM
  3. Service Panel Problem Bryant Breaker Fried
    By Wrex in forum Electrical Forum discussion & Blog
    Replies: 20
    Last Post: 08-16-2008, 08:48 PM
  4. Route question,Light question
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 04-01-2008, 08:49 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •