Thread: The NSPC permits s-traps?

  1. #16
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Quote Originally Posted by Terry View Post
    What you describe on the framing is normal framing. We manage to plumb correctly under those circumstances daily.
    A plumber would have it done in less time that it takes to type this. It's that easy.

    Do you want pipes coming up through the cabinet taking up space?
    It seems a shame to cut up a new cabinet for a pipe that shouldn't have been there.
    The finish carpenter is going to love you for making his job harder.
    I am the finish carpenter. I'm actually interested in learning the proper technique for my personal edification, so if I've missed an easy solution, I want to learn.

    Plumbers typically aren't interested in doing small increments of work, and rightly so, without charging me a hefty flat fee per service call. The nature of my remodel is such that the plumbing, flooring, and the drywall must be done in small increments.

    With a standard installation, I would have to punch a hole into an adjacent cabinet, saw a large hole for the 45 degree vent (I need to offset because I can't shoot straight through the sill plate without cutting a 1" deep channel down my rim joist), and punch a hole for the drain line through the bottom of the adjacent cabinet.

    I could also run the trap arm through three cabinets and into a bearing wall, but I believe this wall sits directly on the main girder.

    Going straight out the back of the sink base cabinet is not possible because the window sill is built up with horizontally stacked 2x4s to accommodate a window that was significantly shorter than the original rough opening. Even if we had cripples below the window instead of solid wood, I'm not sure I could get the vent up to 42" before going horizontal. I would also have to put a 2" hole through 2x4 king and jack studs, which would require some sort of Simpson tie reinforcement.

    If I'm missing a really obvious solution, please let me know. I would prefer to keep all the pvc in one cabinet and drill a single hole in the cabinets.

  2. #17
    Senior Robin Hood Guy Ian Gills's Avatar
    Join Date
    Jul 2007
    Location
    USA
    Posts
    2,781

    Default

    a 2" trap arm/drain is sufficient to avoid siphoning on a 1-1/2" p-trap. Can anyone corroborate with a real-life anecdote?
    A lot is to do with the distance between the trap and the vent. I have a 1.5 inch p-trap on a 1.5 inch pipe for my laundry tub. But it is just over 42 inches away from the vent. The trap gulps after the tub has drained. I am going to have to shorten the distance.

    If you have just shy of five feet of pipe between your trap and your vent then you will need 2 inch pipe. Any more than 5 feet and you will run into the same problems as me.

    Although Table 12.8.1 shows something different. Where am I going wrong here?
    Last edited by Ian Gills; 07-01-2010 at 09:12 AM.

  3. #18
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Well, the table specifies lengths based on the trap arm size (1-1/2" in my case). A 1-1/2" trap corresponds to a developed length of five feet. If the drain is horizontal until you hit the sanitary tee for the vent, you should still have 18 inches to remain code compliant. In fact, according to the table, 42 inches should be fine for 1-1/4". Are you dipping below the crown weir before you tie into the vent? You can have up to 3 DFUs on a horizontal drain, and I believe a standard laundry tub counts for two. I'm not a pro, so I'm not the best one to help you troubleshoot, but I would make sure your vent is clear of obstructions and that the p-trap is not reversed.
    Last edited by Noth Jersey; 07-01-2010 at 09:42 AM.

  4. #19
    TROJAN WORLDWIDE SALES RP MACPLUMB 777's Avatar
    Join Date
    Aug 2007
    Location
    Houston, Texas, United States
    Posts
    631
    Blog Entries
    1

    Default

    I would follow terry's recommendation come out of the top of the tee 90

    over below your

    stacked wood, then outside the window space 90 up though the roof is

    how real plumbers would get it done,

    or install aav on top of the tee as high as possible

    MACPLUMB 777

    E-MAIL
    JERRYMAC@TROJANWORLDWIDE.COM


    35 YEAR MASTER PLUMBER, HEATING, ELECTRIC, DRAINS, FIRE SPRINKLERS, WATER HEATER
    AND BOILERS SINCE JAN, 1989

    281-706-1631 7 DYS A WEEK SALES AND TECH. SUPPORT
    Trojan Worldwide Web Site


     



  5. #20
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Mac,

    The trouble is those stacked 2x4s start at about 38 inches above the finished floor. I'm pretty sure the inspector will not allow me an exception from the requirement to keep that horizontal vent six inches above the flood rim of my fixture. In NJ, we have to have an engineer design the AAV. He might allow me to augment the combination waste-vent type installation, but I'm a little reluctant to introduce a mechanical vent that will one day fail and introduce sewer gas into the house. Do you know of an AAV with some sort of fail-safe, i.e., it automatically closes off when it fails?

  6. #21
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Which ever way you go, could you post some pictures when done?
    Terry

  7. #22
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    Hi guys. Here in Illinois it is against code to run the disposal into a end waste and use a single trap. Each fixture has to have its own trap. The way we do it is a 2" line in the wall come out with a 1 1/2 double Wye. The center of the double Wye would be the clean out, then each side of the double Wye would have a trap. So the picture here is not that far off base to what meets the Illinois plumbing code.


  8. #23
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Quote Originally Posted by Terry View Post
    Which ever way you go, could you post some pictures when done?
    Terry
    If I'm ever done, I'll gladly post some pictures.

    Quote Originally Posted by SewerRatz View Post
    Hi guys. Here in Illinois it is against code to run the disposal into a end waste and use a single trap. Each fixture has to have its own trap. The way we do it is a 2" line in the wall come out with a 1 1/2 double Wye. The center of the double Wye would be the clean out, then each side of the double Wye would have a trap. So the picture here is not that far off base to what meets the Illinois plumbing code.
    Terry and Doherty tell me the type of installation in the picture will result in siphoning. Have you ever experienced this phenomenon with your double wye configuration?
    Last edited by Noth Jersey; 07-02-2010 at 10:55 AM.

  9. #24
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    Quote Originally Posted by Noth Jersey View Post
    If I'm ever done, I'll gladly post some pictures.


    Terry and Doherty tell me the type of installation in the picture will result in siphoning. Have you ever experienced this phenomenon with your double wye configuration?
    Nope never had an issue. As I said its allowed here in Illinois. Its best to check with your local plumbing inspector to see what meets the code by you.

  10. #25
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Why not disconnect the p-trap at the union for a cleanout? What's the benefit of the double wye?

  11. #26
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    There always needs to be a cleanout on a kitchen sink.
    The double wye makes sense too. One trap doesn't run by the other like in the first drawing, it's more like a double fixture fitting in that the arms come in equally and not by each other. The cleanout in the center would be the same in other codes as the clean out either on the arm or on the vertical below.
    Kitchens need cleaning out more then most other fixtures because of the grease, and from the disposers.

  12. #27
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Here's a related thread: http://www.terrylove.com/forums/show...ty-%28again%29

    Here's the relevant NSPC excerpt on the other thread:


    I believe exception number 3 indicates that the end outlet continuous waste fitting is acceptable.

  13. #28
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    It would seem to be true, however we always have to look at the local inspector and please him or her.

    Years ago, I plumbed seven meat markets for a large chain. Since the stores were located in different cities and counties, I had to meet with each local inspector to find out how I was going to pass inspection. Everything was supposed to be UPC code, however I wound up plumbing each one differently.

  14. #29
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    Those prima donnas.

  15. #30
    DIY Senior Member Noth Jersey's Avatar
    Join Date
    Jan 2009
    Location
    Hopatcong, NJ
    Posts
    107

    Default

    I think the branch vent below is very dubious, but how does the rest of the sketch look?

    Name:  Kitchen Sink.jpg
Views: 847
Size:  32.7 KB

Similar Threads

  1. Back dating permits
    By Cookie in forum Remodel Forum & Blog
    Replies: 6
    Last Post: 01-01-2010, 07:27 PM
  2. Traps
    By Mark Chuck in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 12-18-2008, 01:33 PM
  3. Concerning codes, permits, licenses, inspections, ad infinitum
    By leejosepho in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 04-28-2007, 05:08 AM
  4. p traps
    By fyrchyk in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-12-2006, 02:23 PM
  5. Drum Traps
    By Steven Graham in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 10-02-2005, 11:29 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •