Thread: double sanitary tee in Canada

  1. #1
    a/v technician segal46's Avatar
    Join Date
    Feb 2010
    Location
    montreal , QC
    Posts
    19

    Default double sanitary tee in Canada

    Hi all,
    My question pertains to a double sanitary tee 2inch reduced to 1-1/2, i've been searching everywhere in Montreal, seems plumbers here dont like to use it as much as elswhere, though through shipement i will end up paying double for it, sic quebec is distinct for its own reasons...lol.
    How many plumbers use double sanitary tee's and if not why not, i will be using it for 2 sinks in different rooms, leading to a 2 inch drain.
    thanks

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    It, along with a double combination Y-1/8 bend, is ILLEGAL for that use in this, and most areas using the UPC. The IPC might allow it, but I am not sure about that. You are supposed to use the proper fitting, which is a "back to back fixture fitting", (R&G Sloane #91491 in ABS), which comes in 2x2x1 1/2x1 1/2, 2x1 1/2x1 1/2x1 1/2, and all sides 2", plus larger sizes.

    Double fixture cross
    Last edited by Terry; 06-19-2010 at 12:44 PM.

  3. #3
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    unfortunately ( if you are in the drain cleaning game ) IPC allows it
    Perception is 3/4 of reality

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    As you can see, by the insert which was added to my posting, it appears similar to a double combo. However, the branches are attached higher up on the barrel to eliminate the creation of a 3/4 "S" trap, which would occur with a double combo. A sanitary cross is a "terrible" fitting to use in its place because while it is not impossible to snake the vertical line through one, by the time you succeeded you would have called it every name in the book that would have gotten your mouth washed out with soap when you were younger.

  5. #5
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    double san tees are probably the reason why they came up with the drop head for your snake
    Perception is 3/4 of reality

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    Even they do not always work. The spinning head will usually flip up and enter the opposite side.

  7. #7
    In the Trades Wally Hays's Avatar
    Join Date
    Nov 2009
    Location
    New England
    Posts
    652

    Default

    Even better is when the whip around and crack the fitting
    Perception is 3/4 of reality

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    Well, I have never had that happen, but if it did, it would mean the fitting was already done for, and you just helped it along.

  9. #9
    a/v technician segal46's Avatar
    Join Date
    Feb 2010
    Location
    montreal , QC
    Posts
    19

    Default

    Why would I need to fish sinks when they lead to a 2inch vertical drain with a drain plug, they are bathroom sinks hand washing and soap will probably be the worst they see.
    Just a thought to the responses which where somewhat confusing, though I understand by the pic Hj put up the higher curb on the double fixture cross

  10. #10
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    Are you kidding me?
    Have you never snaked a lav drain and seen what comes out on the end of the snake.
    Lavs have nasty stuff. Snaking lavs is one of the most common things I do for people. Many homes have slow lav drains over time.
    That's why plumbers are called in, and when the piping in the wall has the wrong fittings, it creates problems for the life of the home.
    Not just a year or two, for the life of the home.

    I'm getting hungry just looking at this


    Looking inside a sink drain, you know this stuff smells good.


    Stuff we find inside of pipes
    Last edited by Terry; 06-20-2010 at 11:13 AM.

  11. #11
    a/v technician segal46's Avatar
    Join Date
    Feb 2010
    Location
    montreal , QC
    Posts
    19

    Default

    Lmao, point well taken and understood ,guess that's why i,m not a plumber just a do-it your-selfer and seeing that you posted those yummy pictures I will take pride in doing the job right.
    thx
    Sergio

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    A person who uses a sanitary cross for that connection, is usually not experienced enough to KNOW that you also put a cleanout tee below it. I had a motel where EVERY two sink connection was a cross and there were NO cleanout tees. I had to make openings in the wall, and drill a hole in the vent above the fitting to snake it. Then I put a "repair clamp" over the hole to prevent leakage.

  13. #13
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by segal46 View Post
    Hi all,
    My question pertains to a double sanitary tee 2inch reduced to 1-1/2, i've been searching everywhere in Montreal, seems plumbers here dont like to use it as much as elswhere, though through shipement i will end up paying double for it, sic quebec is distinct for its own reasons...lol.
    How many plumbers use double sanitary tee's and if not why not, i will be using it for 2 sinks in different rooms, leading to a 2 inch drain.
    thanks
    Doubt San-T's are perfectly legal here in Canada according to the National Plumbing Code of Canada. In fact if you have two sinks sharing a common vent through a semetrically connected fitting then that fitting HAS to be a Double San-T. Because if it's not you're a creating an S-Trap and you are not allowed to install S-Traps. You also MUST install a cleanout below the Double San-T because every plumbing system needs to be designed so that each and every soil-or-waste pipe can be snaked from inside the house.

    You should be able to find yourself a 2x1.5x1.5" double san-T. If you can't then just buy a 2" double san-t and get three 2x1.5" bushings.

  14. #14
    DIY Member christoff's Avatar
    Join Date
    Dec 2007
    Location
    Toronto Canada
    Posts
    49

    Default

    would my setup work for a lav back to back with a laundry tub,with a cleanout underneath it ?
    Attached Images Attached Images  

  15. #15
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    No. That makes S-Traps what will siphon.

    The vent needs to pull off of the top of the pipe, not six inches lower.

Similar Threads

  1. Double fixture tee or double sanitary tee?
    By nc8861 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 25
    Last Post: 11-03-2011, 11:33 AM
  2. Canada shower question--just wondering
    By timsean in forum Shower & bathtub Forum & Blog
    Replies: 11
    Last Post: 03-12-2010, 12:55 PM
  3. Driven well supply in Alberta or Canada
    By km74 in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 07-14-2008, 07:08 AM
  4. Double Sanitary Tee or Double Wye?
    By MG in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 10-26-2007, 11:45 AM
  5. Venting sizes in Ontario Canada
    By the_slowpoke in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 03-11-2007, 05:25 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •