    Default Check valve doesn't work with Solar Drainback system.

    Hi --

    Looking all over the place for a solution to my problem. Even though I've installed a check-valve, my system "flows" the wrong way at night, sucking hot water out of the tank.

    I have a Radco DBX type drainback system connected with AET panels on the roof. The Radco is a drainback tank with integrated heat exchanger, mounted on the floor next to the water heater, 2 pump setup -- one on the collector loop, one circulating water from the HW heater to the heat exchanger.

    During the day, the system works perfectly. Sun heats the collectors, collector-loop pump works like it should, drainback tank gets hot, circulatory pumps circulate domestic water through the heat exchanger and it heats up. At night, however, the flow reverses... how water leaves the HW heater, circulates the reverse way through the circulatory loop (out the top of the HW heater, through the heat exchanger, into the bottom of the HW heater).

    In other words, at night, I lose some of the BTUs I gathered during the day. I've installed various swing/spring checks, but they don't always shut-off the reverse flow (and, eventually, they go bad and get stuck in the open-position... i guess oxygenated hot-water is a bit corrosive)

    Anyone have an idea how to stop the reverse flow? Do I need to mount the drainback tank above the HW heater?


    Thanks!
    Michael

    PS -- just to be clear -- no flow at night through the collectors. Thermo-syphoning is only occuring on the HW --> heat exchanger loop.Name:  Solar Hot Water Drawing v2.jpg
Views: 1181
Size:  42.9 KBName:  solar_bug.jpg
Views: 801
Size:  74.1 KB
    Last edited by politics123; 06-27-2010 at 11:44 AM.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    INsulate the pipes if they aren't already. IF you are getting circulation, it is because the water in the piping is cooling and creating convection in the pipes. OTHERWISE, the hot water would rise to the top of the loop where the checkvalve is and STAY THERE, since hot water rises. It will ONLY drop down to the bottom of the tank when it cools down.

  3. #3
    DIY Junior Member politics123's Avatar
    Join Date
    Jun 2010
    Location
    virginia
    Posts
    2

    Default

    The pipes are well insulated, but I think it's impossible to prevent any cooling in the pipe... Do you think a couple of vertical loops solve the circulation problem? How high would they need to be?

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    You already HAVE a vertical loop/heat trap. IT is automatic as soon as the pipe turns downward. Water either goes upward when it is heated or downward when it is cooling. IT CANNOT be hot and also flowing downhill.

  5. #5
    DIY Junior Member frankflynn's Avatar
    Join Date
    Oct 2010
    Location
    Palo Alto, CA.
    Posts
    8

    Default

    If your heat exchanger / drain back tank is not lower than the bottom of the hot water heater then you could have some flow trying to equalize the temp.

    I have a somewhat similar system but it is the older direct, drain back (no heat exchanger, domestic hot water circulates in the panels during the day and at night a mechanical valve seals the hot water tank and drains the panels). I also have a check valve which has never given me any problems. It is unusual compared to others I've seen - it looks like a fat bit of pipe, inside is a ball (about an inch diameter - looks like a 'super ball' that we used to play with as kids) and a weak spring on top of it pushing the ball down (closed). Perhaps because the ball os not metal? Perhaps I'm lucky but it's been replaced once in 20 years because the plumber was servicing the big drain back valve (HG Sunspool) and said we should replace everything. It looked pristine to me.

    Finally - are you sure you are seeing backwards flow? In my system flow at night is impossible and I know that it does cool off even when I know no one is home and no hot water is being used.

  6. #6
    DIY Junior Member hickory's Avatar
    Join Date
    Nov 2010
    Location
    Rock Hill SC
    Posts
    1

    Default Solar hot water

    Hi,
    I just had a new solar hot water kit installed. However the back up element seems not to be kicking in and giving me hot water when I need it for a shower. The tank reads 83 F degrees now 11pm EST. and the solar panel on the roof read 43F degrees.
    The way it was designed was to give me hot water whenever I needed it and not have to wait when the sun shines during the day time.
    Any suggestions on what went wrong? How to trouble shoot?
    Thanks,
    JB

  7. #7
    Homeowner Thatguy's Avatar
    Join Date
    Aug 2008
    Location
    MD
    Posts
    1,460

    Default

    Quote Originally Posted by politics123 View Post
    Anyone have an idea how to stop the reverse flow?
    An active control system vs. a passive one.
    I.e., one or more temp. sensors or a flowmeter that detects the reverse flow and controls an electrically operated valve through an electronic interface.
    Temp. sensors & interface parts, $20. Labor, one weekend depending your skill level.

    A single transistor driving the valve may do it. To reduce false alarms we may want to use an AND function with the sensor output and a photocell indicating that the sun has gone down.

    BTW, Jason Bourne I'm not, but with your lat/long given to the precision you gave it in your link, 0.001 degree, I can find your location within +/- 300' or so.

    Quote Originally Posted by hickory View Post
    the back up element seems not to be kicking in
    How many watts, how many volts? Even better, post a schematic.
    Last edited by Thatguy; 11-30-2010 at 02:27 PM.

  8. #8
    DIY Junior Member MikeP860's Avatar
    Join Date
    Nov 2011
    Location
    Brooklyn, CT
    Posts
    2
    Blog Entries
    1

    Default

    Hey Michael! There are two types of check valves. Unless you are powering your circulating pumps through a PV DC (solar panel), you should use the spring type check valves for AC circulating pumps. Another hint is that you should not install a swing type check valve vertically upside down because they have a tendency to hang open. If you are using household current to power the circulating pumps, switch to the "spring" type check valve. Make sure your arrows follow the flow.

Similar Threads

  1. Solar Drainback Water Heating System
    By Alphacarina in forum Solar and Geothermal Water Heating Forum
    Replies: 9
    Last Post: 09-03-2011, 05:46 PM
  2. Swing Check vs. dual check vs. double check valve
    By colbymom in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 25
    Last Post: 05-10-2011, 01:19 PM
  3. Check Valves in Recirc System and Mixing Valve Cause Hammer
    By dwheels in forum Pumps and Tanks Well Forum & Blog
    Replies: 11
    Last Post: 05-15-2010, 09:32 AM
  4. Check valve on a closed loop hydronic system?
    By CHRISUPNORTH in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 11-24-2008, 06:12 AM
  5. Drainback system?
    By gerhard in forum Pumps and Tanks Well Forum & Blog
    Replies: 24
    Last Post: 09-28-2006, 10:03 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •