    Default Condensate Line to Sewer Pipe, NSPC

    Hi everyone, I was searching the internet for some advice and found this site and was hoping you guys could help me out. A little background...I bought a house last June and this past winter I woke up one day and saw a wall with water damage. Turns out my condensate line from the furnace/AC unit that terminates outside froze causing backup into the house. Had a plumber come out and give me an estimate to relocate the pipe inside so it won't freeze. He suggested connecting it to the sewer pipe and using a trap to prevent sewer gas from backing up. Sounds scary to me! Talked to a home inspector friend of mine who said he wasn't crazy about the idea (but has seen it done plenty of times), what if the water in the trap freezes (it's in my attic) then I would have a backup of gas.

    I just want the problem taken care of and am tired of worrying about it. Since it is in my attic, I don't have much choice where to relocate the drain. Any help or comments would be appreciated, thanks!

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    I would trust the plumber.
    They are licensed, which takes 8,000 hours before they can get their card, have to pass a State test, and have education credits.

    Sewer gas in the attic? Is your attic ventilated? Mine is.
    But never mind, plumbing vents extend through the roof so that the smells don't get trapped.
    You could put insulation over the pipe to trap the heat in.
    It's a lot warmer "in" the attic then it is outside.

    He could also find a sink or lav inside the house, cut the wall and add a trap and funnel for the condensate.

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    I assume this condensation is from the flue, because there is NO condensation from the furnace A/C unit in the Wintertime. There are situations where the furnace CAN and WILL draw sewer gas into the building if this is the A/C condensate line.

  4. #4
    Master Plumber-Gas Fitter shacko's Avatar
    Join Date
    Jan 2006
    Location
    Rosedale, Md
    Posts
    561

    Default

    they certainly do produce condensate. Where do you think the term high efficiency condensing furnace comes from?

  5. #5
    DIY Member Lightwave's Avatar
    Join Date
    Aug 2007
    Location
    Vancouver, BC
    Posts
    98

    Default

    Both condensing furnaces and AC coils produce condensate. Both produce condensate only when they are operating: AC in summer, furnace in winter.

    The condensate line on a condensing furnace is connected to the combustion air/flu piping. Because condensing furnaces have a sealed combustion air path, the condensate line has no connection to air inside the house.

    AC condensate lines are directly connected to house ductwork and must be appropriately trapped all year or protected by an air gap. Do not drain AC condensate into DWV piping without ensuring that the trap will remain filled all year. Failure to do so will cause sewer gasses to enter the house.

    Specific requirements apply to trapping draw through AC equipment where the AC coil is on the low pressure (draw) side of the blower. Air handlers are the most commonly found draw through AC equipment. Follow manufacturer instructions or refer to this document from Lennox. Failure to adequately trap draw through AC will prevent humidity removal, could cause water damage to the blower, and will result in sewer gas being drawn into the ductwork by the blower.

    Secondary drain lines must be installed (and trapped) on HVAC equipment installed in an attic or where water leakage could cause damage.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Which is WHY I said I assume the condensate is from the flue. But that would require that it be a condensing unit, and that may, or may not, be what the person has. He does not specify, so we are just guessing.

Similar Threads

  1. “extra” Cast Iron Vent pipe still needed? NSPC
    By CraigNJ in forum NSPC Plumbing Code Questions
    Replies: 4
    Last Post: 06-07-2010, 02:21 PM
  2. “extra” Cast Iron Vent pipe still needed? NSPC
    By CraigNJ in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 06-07-2010, 02:21 PM
  3. Condensate Line
    By schott in forum HVAC Heating & Cooling
    Replies: 11
    Last Post: 07-10-2007, 10:10 PM
  4. Sewer line pipe size
    By Terry in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 06-07-2005, 02:16 PM
  5. Sewer line to city line (sewer lateral) question r/o
    By H20Melon in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-11-2005, 05:12 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •