    Default Contactor replacement

    I had the HVAC guy come out to my place and he told me the contactor and capacitor needed to be replaced. He wrote down the parts I needed and I ordered them from a local appliance store. The new contactor looks much different from my old one and I want to make sure I do it right.

    The two big questions I have are where my yellow wire which was attached to my HI9 goes and I also had a brown wire that was previously attached to the C terminal. My new one doesn't seem to have those labeled.

    Here is a picture of the old one

    The orientation of the old one is the same as in the picture.

    Here is the new one


    I forgot to mention that the HVAC guy said to pull the plug on the furnace before I swapped them out which I did do.

    I found a wiring guide for it and I believe I have it wired correctly, however when I plugged my furnace back in (I followed the instructions on the panel) the fan isn't turning on.
    Last edited by Rickcusaf; 06-03-2010 at 05:20 PM.

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    One key characteristic of a contactor is the coil voltage....can be 24V, 120, or 240. Are you certain that the new contactor has the correct coil voltage.

  3. #3

    Default

    Hard to tell from the photo, but it does not look like the low voltage control wires are attached to the contactor.

  4. #4
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default

    They were disconnected at the time, but I connected them shortly after posting. Right now my biggest problem is that my gas furnace isn't turning on at all. I've used a multi-meter to check my wall voltage and it's good and the next step was to check the slow-blow fuse and it seems a little discoloured, but didn't look bad. I took the fuse out though and tried a direct connection just to see if the lights would come on, but none of the lights on my circuit board are coming on.

    I have a Rheem Criterion II furnace. I've never had a problem with it until I unplugged it. Is there something special I need to do to restart it? I followed the directions on the front before I took it apart, but it doesn't look like power is even making it to the system.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    HOW the wires are connected to ALL the contactor terminals is important, and since the wires have all be disconnected from the old one we cannot tell you the purpose of the various wires, or WHERE they attach to the new relay since we also do not have a diagram of that one. IT is hard to tell, but are the two lower connections tied together with that brass bar and the contactor just switching the upper wire? If, so either you have a 120v system and are switching the neutral, or you have a 240v system and are NOT breaking one of the two feeds. Neither of which is legal, proper, or safe. Probably the worst test to make is to remove/bypass a fuse and then activate the circuit board. If there were a problem, that could destroy the board before you could deactivate the power.
    Last edited by hj; 06-06-2010 at 07:17 AM.

  6. #6
    DIY Junior Member Rickcusaf's Avatar
    Join Date
    May 2010
    Location
    Navarre FL
    Posts
    19

    Default

    Here are pictures of my current setup for my contactor. The wiring mirrors how my old setup was with the exception of the two wires on the side. The original setup had the brown wire on the top portion and the yellow wire on the bottom one. Someone has said that I may need to build a jumper for this contactor, but I don't know where it would have to connect or if that person is even right.







    Last edited by Rickcusaf; 06-07-2010 at 11:49 AM. Reason: Picture resize

  7. #7
    DIY Junior Member Rat's Avatar
    Join Date
    Jun 2010
    Location
    Bertram, Texas
    Posts
    12

    Default

    Quote Originally Posted by Rickcusaf View Post
    Here are pictures of my current setup for my contactor. The wiring mirrors how my old setup was with the exception of the two wires on the side. The original setup had the brown wire on the top portion and the yellow wire on the bottom one. Someone has said that I may need to build a jumper for this contactor, but I don't know where it would have to connect or if that person is even right.


    I see the problem.In this image you have the brown and yellow wire on the contactor hooked to the same side of the coil. These are low voltage wires (24 VAC) and one needs to be on one side of the coil and the other on the other side of the coil. The way you have them here is a direct short, which is why your furnace will no longer power up.

    In the furnace you have a step down transformer, 120V to 24V. Somewhere on the circuit board there is a 3 Amp automotive type fuse that is blown.

    Fix the wires on the contactor, one on each side, then replace the fuse, re-cycle the line power (switch) and it will work.
    There's nothing magical about it; it's all science, physics and math.

Similar Threads

  1. Tub replacement
    By scott99 in forum Shower & bathtub Forum & Blog
    Replies: 27
    Last Post: 10-24-2009, 11:05 PM
  2. tub replacement help
    By jeremytl in forum Shower & bathtub Forum & Blog
    Replies: 8
    Last Post: 10-07-2009, 12:29 PM
  3. TEE replacement
    By linkc101@yahoo.com in forum Irrigation / Sprinkler Forum
    Replies: 10
    Last Post: 03-18-2008, 08:18 PM
  4. Pumptec Plus contactor question
    By xtorq12 in forum Pumps and Tanks Well Forum & Blog
    Replies: 13
    Last Post: 03-13-2008, 08:14 PM
  5. Contactor Question
    By Dungmin in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 11-17-2007, 09:45 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •